T
Member
Each ground wire must be able to handle the full OCPD.

The reason is that in the event of a short in one of the pipes... ALL of the fault current floods the short, which is going to be huge. The grounding conductor in the undamaged pipe has to be able to handle the surge.

Example, a forklift or crane loses a heavy load that crushes surface mounted pipes in parallel... earthquakes... vehicle strikes... errant backhoes... subsidence crushes pipes... landslides...

If something can go wrong, it will. The instantaneous fault energy that is released from a paralleled XFMR faulting is truly astounding.



Tesla
Insulated Tools for Electricians

Insulated Tools for Electricians, Installers & Maintenance Technicians

Joined: Mar 2008
Posts: 27
G
Member
Reminds me of a hoist that we repaired once...two phases in one conduit third phase and neutral in another, only the neutral and the lone phase conduit took another route and was substantially longer to boot.

Just because it looks neat doesn't always mean it's right.


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Mar 2003
Posts: 849
Y
Member
Overcurrent Protection:
240.4(B) 800Amps or less next highest breaker. .
240.4(C) over 800 amps next lowest breaker.
Thus Parallel 500 mcm 380x2 = 760 next highest 800.
800 amp breaker per code.
Thus 4 sets of Parallel 500 MCM = 380 x 4 =1520.
240.6 standard breaker rateings next lowest 1200 .
1200 amp breaker per code.
4 sets 600mcm . 600mcm = 420x4=1680 . next lowest breaker 1600.
1600 amp breaker per code.
When you parallel MC cable above 800 amp you have to either order special cable(larger equipment ground) to comply with the code.
Equipment Ground in EACH conduit per 250.122F
Sized per breaker. As stated in pervious post.