I can't seem to reconcile T 310.15(B)(6) with 110.14(C)(1)(b)(1). What do you think?

This is a residential single phase overhead service drop, going to a GE meter center with feed thru lugs. The 200A main will protect the feeder to a 200A subpanel inside. Local jurisdiction using 2005 NEC.

Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?

Thanks,
Mills

2017 / 2014 NEC & Related Books and Study Guides
Re: Does 310.15 overrule temperature limitations? [Re: Mills] #182187
11/20/08 05:04 PM
11/20/08 05:04 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Two different things.
310.15(B)(6) gives you a break on the ampacity because they know there is a lot of diversity in the total load of a dwelling. You are not using 310.16 at all.


Greg Fretwell
Re: Does 310.15 overrule temperature limitations? [Re: Mills] #182221
11/21/08 09:25 AM
11/21/08 09:25 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by Mills
Does 2005 NEC T310.15(B)(6) allow 4/0 Al for service and feeder, or is that trumped by the manufacturer’s label [Use 60/75C conductors], which would require 250 kcmil?
The safe bet is always to ask your AHJ as theirs is the only opinion that matters, but I concur with Greg, 310.15(B)(6) requires 4/0, and specifically states you don't have to go larger. 310.16 does not apply to this cable.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,027 Are you busy
181,017 Re: Forum
171,265 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.9513 MB (Peak: 1.0788 MB) Zlib enabled. Server Time: 2018-02-20 03:41:03 UTC