Retrofit for old 2 Wire Romex
#182070
11/17/08 12:48 PM
|
Joined: Nov 2004
Posts: 7
OP
New Member
|
Hi,
Besides replacing old 2 wire Romex, are there any retrofit techniques available?
Thanks, Tammy
|
|
|
Re: Retrofit for old 2 Wire Romex
[Re: Tammy Gammon]
#182076
11/17/08 02:15 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
There are ways you can run a separate EGC to each box in most cases but the only real thing you are saving is the cost of the wire. I bet the labor is a wash.
Greg Fretwell
|
|
|
Re: Retrofit for old 2 Wire Romex
[Re: gfretwell]
#182081
11/17/08 05:03 PM
|
Joined: Jan 2004
Posts: 1,507
Member
|
Depending on what you consider retrofit— It is permitted to protect the circuit with a Ground Fault Circuit Interrupter type circuit breaker and this would allow you to install a 3 wire receptacle (2 wire w/ ground) on the circuit and this would be code compliant, if that's what you were interested in. Beyond that, I agree with Greg.
George Little
|
|
|
Re: Retrofit for old 2 Wire Romex
[Re: George Little]
#182090
11/17/08 08:27 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
Usually when I hear this question it is because the customer wants to install something that needs a ground. Most stuff in a home has a 2 prong plug so it is not an issue but when you are installing computers that need surge/EMI protection or equipment with grounded cases there is nothing better than a real hard wire ground ... even if the code allows GFCIs. Bear in mind, in most cases the fault will go through the user to operate the GFCI. I hope they know to test them often.
Greg Fretwell
|
|
|
|
|