Safety at heights?
1 members (Scott35), 507 guests, and 15 robots.
#181965 11/12/08 10:38 PM
cgw Offline OP
When the elevator manufacturer says to not exceed 3% drop in the voltage do they mean at motor start or at the running current?
Based on FLA of the total motor load plus 25% of the largest motor, would be my guess.
Running. You would never meet 3% VD on start.