#182027 11/16/08 01:40 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Does 225.30 allow a person to have a multiwire 15a. circuit to a residential garage and a 50a. Welder outlet? These would be two separate circuits originating at the house. I say no, but there seems to be others that would allow it.


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
The letter of the code would prohibit it.
For that matter could you have a multistation smoke/heat detector system tied to the garage separate from the general use circuit.

In your case I would want a sub panel if this was still in the permit/design phase.
The cost difference would be minimal since you could probably still feed the whole mess with 6ga on a 60 from the house.


Greg Fretwell