#181965 11/12/08 10:38 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
When the elevator manufacturer says to not exceed 3% drop in the voltage do they mean at motor start or at the running current?

Joined: Jul 2004
Posts: 9,662
Likes: 4
G
Member
Based on FLA of the total motor load plus 25% of the largest motor, would be my guess.


Greg Fretwell
Joined: Jun 2007
Posts: 301
J
Member
Running. You would never meet 3% VD on start.