Motor feeder voltage drop #181965 11/12/08 09:38 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
When the elevator manufacturer says to not exceed 3% drop in the voltage do they mean at motor start or at the running current?

Work Gear for Electricians and the Trades
Re: Motor feeder voltage drop [Re: cgw] #181970 11/13/08 02:43 AM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Based on FLA of the total motor load plus 25% of the largest motor, would be my guess.


Greg Fretwell
Re: Motor feeder voltage drop [Re: gfretwell] #182038 11/16/08 02:35 PM
Joined: Jun 2007
Posts: 301
J
JValdes Offline
Member
Running. You would never meet 3% VD on start.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,411 Are you busy
209,304 Re: Forum
196,593 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3