Motor feeder voltage drop #181965
11/12/08 10:38 PM
11/12/08 10:38 PM
C
cgw  Offline OP
Member
Joined: Jul 2004
Posts: 133
Rochester NY
When the elevator manufacturer says to not exceed 3% drop in the voltage do they mean at motor start or at the running current?

Work Gear for Electricians and the Trades
Re: Motor feeder voltage drop [Re: cgw] #181970
11/13/08 03:43 AM
11/13/08 03:43 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,251
Estero,Fl,usa
Based on FLA of the total motor load plus 25% of the largest motor, would be my guess.


Greg Fretwell
Re: Motor feeder voltage drop [Re: gfretwell] #182038
11/16/08 03:35 PM
11/16/08 03:35 PM
J
JValdes  Offline
Member
Joined: Jun 2007
Posts: 301
South Carolina
Running. You would never meet 3% VD on start.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,236
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,590 Are you busy
186,323 Re: Forum
175,782 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9503 MB (Peak: 1.0756 MB) Zlib enabled. Server Time: 2018-08-18 05:10:07 UTC