temperature rating of 40 degrees??? #181869
11/05/08 01:28 AM
11/05/08 01:28 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
I have noticed that many circiut breakers have 2 temperature ratings on them, one is 75 and the other is 40.
Do you guys know what that 40 represents?

Thank you


Be kind to your neighbor, he knows where you live

Work Gear for Electricians and the Trades
Re: temperature rating of 40 degrees??? [Re: Niko] #181870
11/05/08 02:05 AM
11/05/08 02:05 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,324
Estero,Fl,usa
75c is the terminal rating and 40c is the ambient temperature they are calibrated at ... the way I have heard it.


Greg Fretwell
Re: temperature rating of 40 degrees??? [Re: gfretwell] #181872
11/05/08 12:12 PM
11/05/08 12:12 PM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Yep, 75C terminals and 40C ambient. Cabling needs to be derated to never exceed 75C, I'm sure you're familiar with this. Exceeding 40C (104F) ambient, though, can lead to nuisance tripping of the breaker.

Re: temperature rating of 40 degrees??? [Re: SteveFehr] #181874
11/05/08 01:24 PM
11/05/08 01:24 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,324
Estero,Fl,usa
I am still waiting to see what happens when you have a panel stuffed with AFCIs and installed in an un-airconditioned garage.


Greg Fretwell
Re: temperature rating of 40 degrees??? [Re: gfretwell] #181892
11/06/08 07:23 PM
11/06/08 07:23 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
very nice, hey it does not hurt to learn something everyday.
thanks for your time.


Be kind to your neighbor, he knows where you live

Re: temperature rating of 40 degrees??? [Re: gfretwell] #181896
11/07/08 04:00 AM
11/07/08 04:00 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,253
SI,New Zealand
Originally Posted by gfretwell
75c is the terminal rating and 40c is the ambient temperature they are calibrated at ... the way I have heard it.

What temperature (in C) is the conductor insulation rated at?
Reason I ask this, is if you can have up to a 75C connection, what is that actual connection doing to the wire connected to it?
Any heat that comes from a connection, means resistance, and therefore a BAD connection, think pyrolysis.

Re: temperature rating of 40 degrees??? [Re: Trumpy] #181900
11/07/08 09:37 AM
11/07/08 09:37 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
The tempertaure rating of the wire depends on the type of insulation, which is marked on the wire. Probably the most common type used here is THHN/THWN.

THHN/THWN has a 90 degree rating in dry applications, and 75 degree in wet.

The wire can attain those temperatures in a number of ways; generally, the ambient temperature (say, in pipe running across a rooftop) provides a significant rise; simple resistance to the amount of current passing through the wire provides the rest.

Since the temperature rating of the connections is usually lower than that of the wire, we are not able to use the wire to it's fullest potential. That is, we are limited to, say, 65 amps in a wire that otherwise might be rated for 75 amps. Since there isn't a 65 amp breaker out there, if we can't use a 60 amp breaker for the application, we would have to use a larger wire.

Other factors ... wire fill, for instance .... are also considered in 'de-rating' the wires.

While the ambient temperature can cause one section of the wire to be hotter than another, the one factor that heats the entire wire, from one end to the other, is the current carried by the wire. In the example given above, running 75 amps through that particular wire, at room temperature, can easily result in the wire inside conduit reaching 90 degrees - and that's without any connections or splices entering into the equation.

PS: I like the number 17 laugh

Re: temperature rating of 40 degrees??? [Re: renosteinke] #181904
11/07/08 01:29 PM
11/07/08 01:29 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,324
Estero,Fl,usa
I just think of it as a chain with the weakest link determining the ampacity. That can be the real rating or a code mandated rating like you have in most cable wiring methods that put you in the 60c column or 240.4(D) that force the ~80% derating on you in small conductors, no matter what else you have.


Greg Fretwell
Re: temperature rating of 40 degrees??? [Re: gfretwell] #181934
11/10/08 06:54 AM
11/10/08 06:54 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Originally Posted by gfretwell
I am still waiting to see what happens when you have a panel stuffed with AFCIs and installed in an un-airconditioned garage.
I think we already know that answer... CLICK

CLICK

CLICK CLICK ... CLICK

...and that's it. The rest would cool down, see? laugh Thermal derating applies to the temperatures in the panel, not just in the garage. If that environment is going to exceed the rating of the panel, the panel shouldn't be there.

Re: temperature rating of 40 degrees??? [Re: SteveFehr] #181938
11/10/08 08:58 AM
11/10/08 08:58 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Steve - an excellent interprutation of an AFCI in action!

Even without the AFCIs in the panel, 104F is a very easy ambient temperature to reach and excede in many environments. Let alone deserts, you could easily have a panel in direct or partial sunlight in a temperate area reach well above 125F. It's a metal box!

Now add some heat from heavy currents, such as AC, etc. 40C seems like an awful low testing temperature to rate electrical equipment, IMHO.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,253 Are you busy
189,209 Re: Forum
178,892 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 16 (0.004s) Memory: 1.0278 MB (Peak: 1.2101 MB) Zlib enabled. Server Time: 2018-12-17 12:08:30 UTC