Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.
My pvc run will not be underground. Also if it was I am sure you can because it also has THWN classification. Please correct me if I am wrong on this one.
The THWN is the saviour. but I think the Canadian designation is TWN75 as T90 is only ok for damp and dry locations. I presume the wire you have chosen is Dual rated? As for NMD in a raceway You are allowed %53 fill from table 8 for a single multi conductor cable Based on the measured area.