Hi, how do you figure out what size PVC conduit to use if your pulling 6/3 NMWU into it for an outdoor hottub? My guess is to use 1"
Never trust an electrician with no eyebrows!!
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
One inch is too small. It's a fight to get it into a short one inch sleeve. 1.25 inch is minimum but you need at least 1.5 inch if you have an LB.
I just pulled a run into 30 feet of 2 inch with 3 elbows and an LB. I did it alone, so it was probably oversized.
|
|
|
|
Joined: Jun 2007
Posts: 106
OP
Member
|
I am going to just pull in #6 T90 and transition to 6?3 NMD 90 inside the house. Easier by far!
Never trust an electrician with no eyebrows!!
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.
|
|
|
|
Joined: Jun 2007
Posts: 106
OP
Member
|
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan. My pvc run will not be underground. Also if it was I am sure you can because it also has THWN classification. Please correct me if I am wrong on this one.
Never trust an electrician with no eyebrows!!
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
The THWN is the saviour. but I think the Canadian designation is TWN75 as T90 is only ok for damp and dry locations. I presume the wire you have chosen is Dual rated? As for NMD in a raceway You are allowed %53 fill from table 8 for a single multi conductor cable Based on the measured area.
|
|
|
|
Joined: Feb 2003
Posts: 231
Member
|
This page talks about the use of T-90. Building Wire T-90
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
We can't run T-90 outside because of its minimum temperature rating.
|
|
|
|
Joined: Jun 2007
Posts: 106
OP
Member
|
Here in Ontario we are permitted to use T90 underground because it is dual rated. It is also rated TWN75.
Never trust an electrician with no eyebrows!!
|
|
|