#181604 10/18/08 09:50 PM
Joined: Jun 2007
Posts: 106
M
Member
Hi, how do you figure out what size PVC conduit to use if your pulling 6/3 NMWU into it for an outdoor hottub? My guess is to use 1"


Never trust an electrician with no eyebrows!!
Horizontal Ad
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
One inch is too small. It's a fight to get it into a short one inch sleeve. 1.25 inch is minimum but you need at least 1.5 inch if you have an LB.

I just pulled a run into 30 feet of 2 inch with 3 elbows and an LB. I did it alone, so it was probably oversized.

Joined: Jun 2007
Posts: 106
M
Member
I am going to just pull in #6 T90 and transition to 6?3 NMD 90 inside the house. Easier by far!


Never trust an electrician with no eyebrows!!
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.

Joined: Jun 2007
Posts: 106
M
Member
Originally Posted by twh
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.


My pvc run will not be underground. Also if it was I am sure you can because it also has THWN classification. Please correct me if I am wrong on this one.


Never trust an electrician with no eyebrows!!
Joined: Jun 2006
Posts: 613
M
Member
The THWN is the saviour. but I think the Canadian designation is TWN75 as T90 is only ok for damp and dry locations. I presume the wire you have chosen is Dual rated? As for NMD in a raceway You are allowed %53 fill from table 8 for a single multi conductor cable Based on the measured area.

Joined: Feb 2003
Posts: 231
R
Member
This page talks about the use of T-90.

Building Wire T-90

Horizontal Ad
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
We can't run T-90 outside because of its minimum temperature rating.

Joined: Jun 2007
Posts: 106
M
Member
Here in Ontario we are permitted to use T90 underground because it is dual rated. It is also rated TWN75.


Never trust an electrician with no eyebrows!!

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Popular Topics(Views)
558,633 Are you busy
432,923 Re: Forum
401,932 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5