Size of PVC for 6/3 NMWU #181604 10/18/08 09:50 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
Hi, how do you figure out what size PVC conduit to use if your pulling 6/3 NMWU into it for an outdoor hottub? My guess is to use 1"


Never trust an electrician with no eyebrows!!
Tools for Electricians:
Re: Size of PVC for 6/3 NMWU [Re: mr_electrician] #181608 10/19/08 07:49 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
One inch is too small. It's a fight to get it into a short one inch sleeve. 1.25 inch is minimum but you need at least 1.5 inch if you have an LB.

I just pulled a run into 30 feet of 2 inch with 3 elbows and an LB. I did it alone, so it was probably oversized.

Re: Size of PVC for 6/3 NMWU [Re: twh] #181609 10/19/08 07:56 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
I am going to just pull in #6 T90 and transition to 6?3 NMD 90 inside the house. Easier by far!


Never trust an electrician with no eyebrows!!
Re: Size of PVC for 6/3 NMWU [Re: mr_electrician] #181611 10/19/08 09:15 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.

Re: Size of PVC for 6/3 NMWU [Re: twh] #181613 10/20/08 06:20 AM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
Originally Posted by twh
Can you install T90 in an underground PVC run? We can't even install it outside in Saskatchewan.


My pvc run will not be underground. Also if it was I am sure you can because it also has THWN classification. Please correct me if I am wrong on this one.


Never trust an electrician with no eyebrows!!
Re: Size of PVC for 6/3 NMWU [Re: mr_electrician] #181619 10/20/08 11:29 AM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
The THWN is the saviour. but I think the Canadian designation is TWN75 as T90 is only ok for damp and dry locations. I presume the wire you have chosen is Dual rated? As for NMD in a raceway You are allowed %53 fill from table 8 for a single multi conductor cable Based on the measured area.

Re: Size of PVC for 6/3 NMWU [Re: mikesh] #181670 10/22/08 04:32 PM
Joined: Feb 2003
Posts: 231
R
RobbieD Offline
Member
This page talks about the use of T-90.

Building Wire T-90

Re: Size of PVC for 6/3 NMWU [Re: RobbieD] #181675 10/22/08 08:01 PM
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
We can't run T-90 outside because of its minimum temperature rating.

Re: Size of PVC for 6/3 NMWU [Re: twh] #181684 10/23/08 01:55 PM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
Here in Ontario we are permitted to use T90 underground because it is dual rated. It is also rated TWN75.


Never trust an electrician with no eyebrows!!

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,469 Are you busy
209,379 Re: Forum
196,651 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3