ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Tiny Homes and the NEC
by gfretwell - 12/06/22 01:43 AM
EMC Glands on Motors
by Trumpy - 12/01/22 06:12 AM
Ground Rods: Installation and Hook-Up
by Trumpy - 12/01/22 05:54 AM
Happy Thanksgiving all!
by gfretwell - 11/30/22 05:55 PM
Colt Firearms Switchbox
by NORCAL - 11/29/22 01:04 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
1 members (Scott35), 28 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
How to size the Collector Bus?
I have 3 1600kw/400V gengerators Synchronized and connected to the Collector Bus.

Joined: Jun 2006
Posts: 613
M
Member
Ok I'll bite, (1600 X 125%) + 1600 + 1600 = 5200 amps.
28-108 of the Canadian Electrical code for conductor sizing for Motors.

Method 2 take the connected load at 125% and size the bus for that.

I don't know what a collector bus is but i guessed it is the bus after the transfer switches where each generator parallels.

Joined: Feb 2008
Posts: 12
T
theseus Offline OP
Member
Yes,Collector bus = paralleling bus.

But,generator is different from motor.

Joined: Jun 2006
Posts: 613
M
Member
Yes a generator and a motor are not the same but the wires are sized the same. At least that is what i derive from section 28 of the CEC %125 of the first (largest) generator and 100% of the next 2. Generators and motors are very similar in terms of what happens inside them whether making or using electricity. Cooling, winding and loading all apply the same. A stator for a motor and a generator look the same from a winders perspective at least from 28 year old memories they do. I have rewound stators for both. The armatures are different as there is excitation and magnetic fields to build.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,432
Joined: July 2002
Top Posters(30 Days)
Trumpy 9
NORCAL 3
Popular Topics(Views)
300,591 Are you busy
230,281 Re: Forum
215,052 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5