Securing lay in light fixtures #180414
08/25/08 02:15 PM
08/25/08 02:15 PM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
Somehow I was under the impression that lay in light fixtures had to be secured by individual wires from a main support above the ceiling. I'm aware that they are to be secured to the "framing members" by screws, rivets, etc....
I'm looking in the 2005 code and that's all I see. Am I missing something? Thanks, Steve....

2017 / 2014 NEC & Related Books and Study Guides
Re: Securing lay in light fixtures [Re: sparkync] #180418
08/25/08 02:59 PM
08/25/08 02:59 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,035
Brick, NJ USA
Steve:
NEC says what you listed above. Seismic code/building or fire may require independent support. Lastly, plans may require it in the spec; or the ceiling grid mfg may have it in the mfg installation instructions.


John
Re: Securing lay in light fixtures [Re: HotLine1] #180429
08/26/08 09:49 AM
08/26/08 09:49 AM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
HotLine's got it right, especially out here on the West coast. Your building and seismic codes dictate much more of the overhead support requirements than your NEC and electrical inspector.

If there is any question about the requirements in your area, contact your AHJ as early in the job as possible to avoid going back for a red tag from someone you don't expect.

Good Luck!

Re: Securing lay in light fixtures [Re: Zapped] #180600
08/31/08 09:50 PM
08/31/08 09:50 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 849
Michigan
300.11 (A) 1(Fire -Rated assemblys ) 300.11 (A) 2 Non-Fire -rated. Handbook covers it quite well,
also 410.16.
More or Less says UNLESS ceiling assembly has been Tested and Listed for that use. Support wires are required & must be marked by color or tagging.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,370 Are you busy
187,982 Re: Forum
177,527 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 15 (0.013s) Memory: 0.9603 MB (Peak: 1.0928 MB) Zlib enabled. Server Time: 2018-10-18 05:04:00 UTC