Tap rule, Which is appropriate? #180220 08/18/08 07:03 PM
Joined: Jun 2007
Posts: 20
A
Angel_Electric Offline OP
Member
I've Installed a transformer that on the secondary has nearly 36' of wire parallel feeding a 120v/208v panel. The engineer over seeing the job has quoted the reference in the code on a particular 10' rule. The problem I have with this rule is there are additional rules dictating that 25' is acceptable ,how does one go about determining whether the 10' or 25' apply. Either way I believe I'm going to be required to put a disconnect at the transformer.

2017 / 2014 NEC & Related Books and Study Guides
Re: Tap rule, Which is appropriate? [Re: Angel_Electric] #180224 08/18/08 08:07 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Ever wonder why the tap rules are all referred to according to the length of the tap? Did you also notice that the distances, and other conditions, are more limited the longer the tap?

If you can't reach it with a ten foot tap, you can't use the ten foot rule.

Re: Tap rule, Which is appropriate? [Re: renosteinke] #180226 08/18/08 08:16 PM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
The tap rules are in Article 240.21, and include the 25' tap rule, among others.


Re: Tap rule, Which is appropriate? [Re: Angel_Electric] #180228 08/18/08 08:42 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
[quote=Angel...how does one go about determining whether the 10' or 25' apply.[/quote]

The simple differences are:
10' tap rule conductors can be any size.
25' tap rule requires the conductors to be a minimum of 1/3 the transformer capacity

Re: Tap rule, Which is appropriate? [Re: JBD] #180230 08/18/08 10:25 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
Is this an inside or outdoor tap? Looks like we are limited to a max of 25' for all secondary conductors unless it is an outdoor installation.


240.21(C)(1) through (C)(6)


George Little
Re: Tap rule, Which is appropriate? [Re: George Little] #180231 08/18/08 10:36 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
More on Transformer Secondary taps:

Just read the original post and the issue is what is the length of the tap.

The tap measurement is to my understanding the length of wire, not the raceway.

For a 10' tap to a 100a. "device" requires 100a conductors, even though the load may only be 75a and it is fused at 80a. If it's a CB than the tap can sized at 80a.

240.21(C)(2)(1)b.
See definition of Device in Article 100


George Little
Re: Tap rule, Which is appropriate? [Re: George Little] #180351 08/23/08 04:18 AM
Joined: Jun 2007
Posts: 20
A
Angel_Electric Offline OP
Member
The problem originated when we had to place a transformer into the nearest gap nearly 28' from where it was shown on the print . The engineering shown placed the transformer suspended into the air ,supported from the building steal. When we went to place this 112kva trans into the air the GC. proclaimed that the structural engineer will not allow us to suspend the trans from the steal because its to heavy. Now the electrical engineer has said we don't comply with the 10' tap rule. I feel
that even though the length of the secondary taps are 26' that we may comply with the 25' tap rule. Basically I have to size the wires according to the percentage ampacity given for the conductors for the 25' rule verses the 10' rule.
Next realization being is that we sized the wires according to the line diagram the electrical engineer specified, and he is probably aware that the wires may only comply with the ampacity of the 10' rule. Solutions ? Move transformer back to where it is shown on print? Build a shelf? Comments appreciated

Re: Tap rule, Which is appropriate? [Re: Angel_Electric] #180352 08/23/08 05:24 AM
Joined: Dec 2000
Posts: 4,287
electure Offline
Member
Originally Posted by Angel_Electric
I feel that even though the length of the secondary taps are 26' that we may comply with the 25' tap rule. Basically I have to size the wires according to the percentage ampacity given for the conductors for the 25' rule verses the 10' rule.


Sure....26' is not 25' or less.

Solution = Let the GC worry about it, and between the EE and the Structural Engineer not doing their jobs properly, let them come up with a fix.

Don't try to "save the day" yourself, you'll be rewarded with only headaches.

Re: Tap rule, Which is appropriate? [Re: electure] #180356 08/23/08 08:16 AM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
This situation is what change orders were created for!

The solution is simple: You need to add over-current protection at some point that will let you meet the 25 ft rule. Or, even, the 10 ft rule. A disconnect with fuses would accomplish this.

Re: Tap rule, Which is appropriate? [Re: renosteinke] #180435 08/26/08 10:49 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
Or just larger cabling- if the cable meets the full ampacity of the main OCP, it's not a bus tap, it's merely an extension of the bus.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,539 Are you busy
209,439 Re: Forum
196,834 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3