Emergency lights on dedicated circuit #179942
08/06/08 07:33 PM
08/06/08 07:33 PM
F
frankgi  Offline OP
Member
Joined: Nov 2005
Posts: 11
NJ USA
I recently failed an inspection because the existing exit/emergency lights were on a dedicated circuit with a sp breaker lock. I was told that circuit needed to be tied in with a breaker that controls a row of lights in the vicinity of 2 emergency lights.(There are other e/e's throughout the building....a liquor store) Customer turns the fixtures on and off by the breakers. Just wondering if Art#700.12(F):exception would apply? Light fixtures and e/e's originate from the same panelboard. There are more than 3 rows of lights. My remedy was to tie e/e circuit in with a row of lights to be left on 24/7.
Any thoughts?
Thanks!


"Its all about the small details"
2017 / 2014 NEC & Related Books and Study Guides
Re: Emergency lights on dedicated circuit [Re: frankgi] #179946
08/06/08 09:05 PM
08/06/08 09:05 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,092
Brick, NJ USA
OK, a plain english explanation....

One open large area/room/store/office, etc.
IF three (3) or more lighting circuits in that 'room', you are allowed to have a 'dedicated' exit/em circ w/cb lock.

IF NOT, the exit/em lighting has to be circuited (connected) to the local lighting circuit, before any switch.

You also mentioned 'existing'; did you touch, modify, relocate, or not touch it?
Usually, a retail store falls under the 'more than three (3) circuits', and has a dedicated exit/em circuit with the 'nite lites'. The number of 'rows' is not really relevant, it's the # of lighting circuits.

What part of NJ are you in ?? And what Article was cited? and by who, Elec, Fire or Bldg?






Last edited by HotLine1; 08/06/08 09:07 PM.

John
Re: Emergency lights on dedicated circuit [Re: HotLine1] #179948
08/06/08 09:28 PM
08/06/08 09:28 PM
F
frankgi  Offline OP
Member
Joined: Nov 2005
Posts: 11
NJ USA
>You also mentioned 'existing'; did you touch, modify, relocate, or not touch it?
Usually, a retail store falls under the 'more than three (3) circuits', and has a dedicated exit/em circuit with the 'nite lites'. The number of 'rows' is not really relevant, it's the # of lighting circuits.

Hi and thanks for your reply.
Just added 1 exit/em with a dual remote head outside, from existing exit/em dedicated circuit. Easily more than 10 lighting circuits from panel. (1 circuit per row)

>What part of NJ are you in ?? And what Article was cited? >and by who, Elec, Fire or Bldg?

SJ.... Art 700 .....Elect
FrankG


"Its all about the small details"
Re: Emergency lights on dedicated circuit [Re: frankgi] #179955
08/07/08 08:01 AM
08/07/08 08:01 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,092
Brick, NJ USA
Best solution...call and speak to the elec inspector, explain that there are more than 3 circuits, the e/e is dedicated, and there is a breaker lock. Conformance with Art 700 IMHO, from your explanation.


John
Re: Emergency lights on dedicated circuit [Re: HotLine1] #179964
08/07/08 03:17 PM
08/07/08 03:17 PM
F
frankgi  Offline OP
Member
Joined: Nov 2005
Posts: 11
NJ USA
Thanks John.
FrankG


"Its all about the small details"

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,884 Are you busy
191,858 Re: Forum
181,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.9698 MB (Peak: 1.1095 MB) Zlib enabled. Server Time: 2019-06-27 11:22:52 UTC