GFCI's and Aluminum Wire #179761
07/30/08 05:01 PM
07/30/08 05:01 PM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
It finally happened .... I came across some aluminum wire in a trailer. Now the fun begins.

For those who have not worked on trailers, they are typically glued together. As a result, opening the walls really isn't an option, and re-pulling the wires is problematic - unless you want to demolish the trailer, and start over!

So, I'm doing the next-best thing ... replacing what wire I can find, and using Co/Alr rated devices. Here's where the trouble begins ....

My local parts houses scratch their heads at the request for rated GFCI receptacles. Leviton assures me that there is no such thing - at least, in their inventory.

Does anyone have a source for Co/Alr rated GFCI's?

(FWIW, this trailer was made before GFCI's were required. While I have 'normal' device boxes, I really want to add GFCI's to the kitchen and bathroom).

Work Gear for Electricians and the Trades
Re: GFCI's and Aluminum Wire [Re: renosteinke] #179762
07/30/08 05:55 PM
07/30/08 05:55 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Would it be possible to use a pigtail of copper (with approved splicing methods)?

Re: GFCI's and Aluminum Wire [Re: renosteinke] #179763
07/30/08 05:58 PM
07/30/08 05:58 PM
dougwells  Offline

Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
How about the dead front (faceless) gfci devices mounted at the panel location for those circuits. Run copper from the Panel to gfci device and an approved method for pig tailing Al to Cu at the GFCI device near panel

Re: GFCI's and Aluminum Wire [Re: dougwells] #179766
07/30/08 06:49 PM
07/30/08 06:49 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Wow, that is a really good one. I can honestly say that I've never encountered this situation. I'm in agreement that finding CO/ALR rated GFI receptacles is likely impossible. I can only imagine an approved method of pigtail splicing and more than likely......an extension box.


---Ed---

"But the guy at Home Depot said it would work."
Re: GFCI's and Aluminum Wire [Re: EV607797] #179767
07/30/08 07:21 PM
07/30/08 07:21 PM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 876
In chat you said that the panel is Zinsco, is the panel going to be replaced? If so, how about a GFCI circuit breaker????

Re: GFCI's and Aluminum Wire [Re: NORCAL] #179771
07/30/08 08:48 PM
07/30/08 08:48 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
I guess it comes down to how many Alumiconns you can get in a box with a GFCI. I see a 1900 box and a ring in your future. wink


Greg Fretwell
Re: GFCI's and Aluminum Wire [Re: gfretwell] #179773
07/30/08 08:56 PM
07/30/08 08:56 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
I was half kidding in that last post but if you gave them a quad with a GFCI and a CO/ALr receptacle you would only have one pair of splices. Splice L/N into the GFCI and use copper jumpers between the receptacles.


Greg Fretwell
Re: GFCI's and Aluminum Wire [Re: NORCAL] #179775
07/30/08 09:01 PM
07/30/08 09:01 PM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Alas, try as I might, I can find nothing wrong with the panel ... plus, with it installed indoors, recessed into the wall, AND it being a trailer (nearly impossible to patch) ... I'm not about to change it. Zinsco lives on ...

Today was productive, in that I now have a very good idea as to what is wrong with the trailer. This, my friends, is why you need to have a megger!

Anyway, I need only replace two sections of wire. Naturally, the least accessible one is guarded by a 35 pound black widow spider ... at least, that's how it looked while I was under the trailer. I just PRAY the brick I hit it with didn't just make it mad! laugh

So, it looks like I'll be doing a fair amount of pigtailing. Apart from the GFCI's, I'll need to do this at the light fixtures.
The King "AlumiConn" connectors look to cost in the neighborhood of $3 each. That's ten bucks' of connectors in a box. I suspect I'll be 'daisy chaining' the $2.60 Cu/Alr devices, rather than my usual pigtail method.
T&B, who had assured me at "counter day" that I would have no trouble getting their rated "Marrette" connectors (about 40 cents each) is proving elusive, now that I actually want some.

Re: GFCI's and Aluminum Wire [Re: renosteinke] #179778
07/31/08 06:13 AM
07/31/08 06:13 AM
M
mbhydro  Offline
Member
Joined: Feb 2003
Posts: 349
Winnipeg MB Canada
Have you tried looking at the "Big Box" stores for the cu/al Marette's, if your wholesaler doesn't have them?

Where I am here in Canada they are on the shelves with the regular ones.

Re: GFCI's and Aluminum Wire [Re: mbhydro] #179782
07/31/08 09:59 AM
07/31/08 09:59 AM
renosteinke  Offline OP
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Thanks, MB .... but, alas, they seem to be a 'marketed in Canada only" product. I'm still looking.

Leviton, P&S, and Hubbell have all informed me that they have no GFCI's rated for aluminum wire.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,599 Are you busy
180,406 Re: Forum
170,869 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.043s Queries: 16 (0.005s) Memory: 1.0287 MB (Peak: 1.2105 MB) Zlib enabled. Server Time: 2018-01-23 13:49:48 UTC