1. Assume a house has a ufer and the water and gas are done in plastic or the flexible gas pipe. Neither are metal, do we still have to bond them?
2. Protecting the main grounding electrode conductor with conduit, etc. pertains to what sizes of conductor?
Thanks, Byron
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: bwise121]
#179394
07/10/08 05:53 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
If the interior piping is plastic how would you bond it?
Greg Fretwell
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: gfretwell]
#179396
07/10/08 06:32 PM
|
Joined: Sep 2003
Posts: 114
OP
Member
|
the stubs under sinks are copper. But I really don't see any point in doing so...just asking.
Thanks
|
|
|
Re: Two questions and where to find the answers -
[Re: bwise121]
#179400
07/10/08 07:29 PM
|
Joined: Jul 2004
Posts: 9,571
Member
|
It is not really a code issue but I would still bond a steel sink to the EGC of the counter receptacles via the copper piping. I couldn't cite a code section tho. I have a stainless counter top and sink in my kitchen and it is bonded to the cooktop EGC (no neutral load) and receptacle EGCs.
If you have a disposal it is probably bonding a steel sink.
... but I am a bonding freak. The steel in my driveway is bonded.
Greg Fretwell
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: bwise121]
#179403
07/10/08 09:59 PM
|
Joined: Jul 2007
Posts: 1,335
Member
|
1. Assume a house has a ufer and the water and gas are done in plastic or the flexible gas pipe. Neither are metal, do we still have to bond them? Nope, how? 2. Protecting the main grounding electrode conductor with conduit, etc. pertains to what sizes of conductor? All of them. 250.64
"Live Awesome!" - Kevin Carosa
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: sparkyinak]
#179407
07/11/08 08:42 AM
|
Joined: Aug 2001
Posts: 457
Member
|
I believe that there are bonding requirements for the CSST? flexible gas lines. These may come from the piping manufacturer, not the NEC. After looking found this. http://www.toolbase.org/pdf/techinv/csst_lightningconcerns.pdf
Last edited by Jim M; 07/11/08 08:43 AM. Reason: added pdf link
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: Jim M]
#179408
07/11/08 11:30 AM
|
Joined: Mar 2005
Posts: 212
Member
|
I think Sparky's answer is oversimplified. It's never wrong to protect them with conduit as long as a steel conduit is choked on both ends, but 250.64 (B) certainly says that there are situations where a grounding electrode conductor size 6 or larger may not require conduit as a means to physically protect it. Guys?
|
|
|
Re: Two questions and where to find the answers - NEC
[Re: Gregtaylor]
#179410
07/11/08 06:31 PM
|
Joined: Jul 2007
Posts: 1,335
Member
|
When not subject to physical damage. A common issue I see in unprotected grounds is exposure to weed whacking and brushing around the ground wire.