250 hp 480 volt three phase 302A 302x125%= 377.5 = 3-500mcm &Gr(per 250.122). 3 inch conduit Breaker 600A. 125 Hp480 volt 3 phase 156 A 156x125%=195amps = 3-3/0 plus gr. 2 inch conduit Breaker 250 amp both either soft starts or VFD. Wanna check my work guys. Hair line between Pride & stupidy Right!!!
What kind of breaker? What environment? Wet? Dry? What ambient temperature? What type of insulation on the conductors? No mention of overloads. Details, Ernie, details- You know how I am.