ground wires from different circuits in same box #178029 05/21/08 05:39 PM
Joined: Aug 2002
Posts: 402
J
jdevlin Offline OP
Member
I am having a debate on another site about ground wires. Can anyone give a code reference that requires all the ground wires one jbox from different circuits to be tied together. Or one that requires them not be tied together.

2017 / 2014 NEC & Related Books and Study Guides
Re: ground wires from different circuits in same box [Re: jdevlin] #178045 05/22/08 05:53 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
I don't think you'll find one. The only real requirement is that they all be electrically connected. So, you can tie them all together, or not tie them together, and it's all the same since they all tie back to the EGC.

Now... you *may* run into issues mixing high and low current circuits and ground paths- if you have a 20A and a 200A circuit going into a single metal box, the metal box is required to be grounded, and I'd argue that any metal in the box- including the bare #12 conductor- is "likely to become energized" and would be required to withstand the fault current from the 200A circuit ...which would require bonding the #12 and #6 ground conductors. So, in that case, 250.122 would apply. Although it *still* doesn't require them to be bonded, it's just the practical thing to do.

Might also come into play if you're mixing #12 and #14 in a box.

Re: ground wires from different circuits in same box [Re: SteveFehr] #178047 05/22/08 06:20 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes.
Where circuit conductors are spliced within a box, or terminated on equipment within or supported by a box, any equipment grounding conductor(s) associated with those circuit conductors shall be connected within the box or to the box with devices suitable for the use in accordance with 250.148(A) through (E).


Don(resqcapt19)
Re: ground wires from different circuits in same box [Re: resqcapt19] #178060 05/22/08 12:42 PM
Joined: Aug 2002
Posts: 402
J
jdevlin Offline OP
Member
This is the article the other person is citing as requiring them to not be connected. He is saying the "associated with those circuit conductors" only refers to each individual circuit not all the separate circuits in the same box.

Re: ground wires from different circuits in same box [Re: jdevlin] #178061 05/22/08 12:51 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
250.148. Only exception is isolated grounds


"Live Awesome!" - Kevin Carosa
Re: ground wires from different circuits in same box [Re: sparkyinak] #178075 05/22/08 07:06 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
Let's remember that the OP is in Canada. I don't think that our article 250 holds much weight north of the border.


---Ed---

"But the guy at Home Depot said it would work."
Re: ground wires from different circuits in same box [Re: EV607797] #178085 05/22/08 09:11 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
Dang it I fell for it again! smile I usually look for that. It was posted in the 2008 NEC discussion forum.


"Live Awesome!" - Kevin Carosa
Re: ground wires from different circuits in same box [Re: sparkyinak] #178105 05/23/08 12:27 PM
Joined: Aug 2002
Posts: 402
J
jdevlin Offline OP
Member
This is an NEC issue NOT a Canadian issue. It is a discusion I am having at a DIY site trying to convince them that all grounds from different circuits should be connected together or find out if they shouldn't be connected. I always thought they should be.

Re: ground wires from different circuits in same box [Re: jdevlin] #178111 05/23/08 04:19 PM
Joined: Apr 2003
Posts: 139
B
BPHgravity Offline
Member
[Linked Image from 1.1.1.2]


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Re: ground wires from different circuits in same box [Re: BPHgravity] #178114 05/23/08 06:00 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
Regardless of the country, and whether you are an electrician or not, let's stop and think about this for a minute:

Say you have a two-gang metal box in a kitchen housing a switch for the light over the sink (on the lighting circuit) and a receptacle on one of the small appliance circuits. Using Romex (Loomex), how in the world could you possibly keep the grounds separated? Even if you didn't bond them together, there's no chance that those bare conductors aren't going to meet, either by touching the box directly or via the grounding connections to the device yokes. The separate grounds are going to meet at some point. I'd tend to think that an intentional bonding of EGCs would be better than those that may occur through unintentional contact.

I think that with this being said, the answer is obvious.

I think that any code that requires that such circuits be kept separate would be impossible to enforce unless separate device boxes were mandated for separate circuits. It would be even more difficult to comply with such a requirement. I think that pretty much sums up the answer to the original question.


---Ed---

"But the guy at Home Depot said it would work."
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,721
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,440 Are you busy
209,338 Re: Forum
196,620 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3