I often see pipes mounted on the wall that have LBs where an LR or and LL would have made the cover more accessible. I always thought this was just a hack by somebody too lazy to get the proper fitting, until....
We had to pull three #4s and a ground into an 1&1/4" pipe and somebody got the bright idea of puting an LR at a corner (no, it wasn't me, but I thought it was a good idea, too.)
I have pulled 500s that went into the pipe easier than those stupid wires went around the corner of that LR. Was this a fluke, or is it just generally a bad idea to use LL/LR fittings on anything larger than maybe #10 or #8? Should I adopt the practice of using sideways LBs for all big wire?
-John
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
If you really want an LR, oversize it and use reducer bushings. The extra space makes it a lot easier. A junction box is even better and they cost less than an LB.
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Conduit bodies are nearly always a PITA ... especially if there's one at either end of the pipe!
If you MUST use one, it's best to arrange the pull so that the wire enters the box from the short side, and exits the long side. When the pull is nearly complete, a tug from the end where you first began will pull the wires in nice, straight, and tight.
However, I prefer to use a box in place of the bodies for the smaller pipe sizes, and a short piece of gutter for the larger sizes. Not only is the pull easier, the final install looks cleaner too!
|
|
|
|
Joined: Nov 2002
Posts: 174
Member
|
|
|
|
|
Joined: Dec 2003
Posts: 36
Member
|
I just got some of those Anybody's in and they seem to work good. But like what others already have said it is tougher to pull around an LR than an LB
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
The Anybody is too ugly to use anywhere that it might be seen. It is a good idea, though.
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
Anybody ever use LBD's? Use a size larger than the conduit you're running and RE down the hubs.... Much easier to get the covers on with large wire pulls vs. a standard LB Crouse Hinds LBD We also use LL's LR's T's, TB's TA's, etc. out where I work.. Many tight spots and these all must remain accessible
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
I avoid LRs and LLs if possible and never use them if the wires are larger than #10. As far as the use of the LBDs or oversized LBs, in many cases this is required by the code rules. Conduit bodies are covered by 314.28. If you are using an LB with #4 or larger conductors and the LB is not marked for the maximum number and size of conductors then the LB must comply with the size requirements found in 314.28(A)(2).
Don(resqcapt19)
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
We sold a lot of these Mogul conduit bodies at Appleton Electric when the NEC changed to require them back several cycles ago. My favorite was the BUB, which had the cover at 45 degrees. A pull in either direction was a straight shot without hitting the wall of the casting.