Thur experience for Cost (Material & Labor) what have you found to be the most cost effective combination of pipe & wire??? Pvc Sch. 40 with Alum or Copper . I;m looking for 3000 amps. Another words 500 mcm , 750, 1000 copper or alum.
4 wires in a conduit. Useing 310.16 75C & 110.14c for terms.
Yoopers
Also mostly 480 volt loads so Neutral can be 12 1/2 percent of phase conductors right.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Dec 2000
Posts: 4,288
Member
Didn't you already ask this question back in February?

Joined: Nov 2000
Posts: 2,148
R
Member
I'd take a look at bus duct for that size feeder.


Don(resqcapt19)
Joined: Mar 2003
Posts: 849
Y
Member
One I posted in Feb was a bit different , Just wondering thur experience which way worked out better.never to proud to learn. Right

Joined: Jun 2004
Posts: 1,273
T
Member
At 3000 Amps your 'window' becomes restrictive, you'll need to stuff 400 Amps in each of eight pipes. That means that you might be forced to go with copper in schedule 40 PVC.

By comparison, bus duct can be had at 3000 Amps in AL.

The shorter path and cheaper conductor makes bus duct a serious competitor.


Tesla
Joined: May 2005
Posts: 984
G
Member
Another consideration with bus duct is the difference in labor hours. Slap up 1 10' length of bus duct and you're done with 10' of feed. For 10' of conduit you still have to pull and terminate the wires...PLUS you have multiple sets of everything.


Ghost307
Joined: Mar 2003
Posts: 849
Y
Member
Cost of Buss Duct custom made otta this world .

Joined: Jan 2004
Posts: 1,507
G
Member
Ernie- You've left out some details (as usual) and I wonder if the question factors in the grounding conductor? With metal raceway - no ground wire- with non-metallic you will need a ground wire- since this is not service. Right? Wrong?


George Little
Joined: Nov 2000
Posts: 2,148
R
Member
How long is the total run? You have to watch out for the length difference with parallel runs.


Don(resqcapt19)
Joined: Mar 2003
Posts: 849
Y
Member
George
Service conduits from utility Co, transformer to Service gear that means NO GROUND WIRE.
Total run is Aprox. 40feet and yes I know about requrements of Parrell runs.
Buss 90's if you've ever installed then cost a bundle as well as regular buss. But I agree worth a price compaireson.

Last edited by Yoopersup; 05/08/08 08:59 AM.
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,407
Joined: July 2002
Top Posters(30 Days)
dsk 7
andey 1
Popular Topics(Views)
284,956 Are you busy
217,489 Re: Forum
203,777 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5