#177101 04/22/08 06:05 AM
I'm Studying a book Called Electrical Wiring Commerial 13Th. Edition.I've run into a formula for voltage drop.The variable (K)is unknown to me and the book does not reference where, why or how its use has derived.The formula is VD=2xKxDxI/Cm. Does anyone Know of an explicit reference for this (K). Thanx
VD=2xKxDxI/Cm
I= Current
2= round trip loss (you'd use 1x if it was a balanced wye circuit)
KxD/Cm represents the resistance of this wire.
Voltage Drop = 2x Current x Resistance
D=length of wire
K/Cm=resistance per unit length.
K is the unit resistance of copper per circular mil
Cm is circular mills of the conductor. (roughly 2.8 Ohms/kcmil/100 feet DC) This equation is only accurate for DC. You can approximate AC (K is roughly 1.3 for AC), but it varies by cable size due to skin resistance and isn't terribly accurate.
This entire value (the resistance per unit length) can simply be looked up in NEC Tables 8 & 9, though. Really, you should also be adjusting it forpower factor and the type of conduit it's in and wire temperature, too, but usually if you have to go into that much detail, you should be upsizing anyhow.
Try my latest presentation based on the NEC at:
http://www.electrician2.com/voltdrophtml/frame.htm
Tools for Electricians
2023 NEC + Exam Prep Study Guides Now Available!
2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman
renosteinke
renosteinke
Blue Collar Country
lemahj 3
311,332 Are you busy
237,652 Re: Forum
221,415 Need opinion