#176830 04/14/08 02:51 AM
Joined: Apr 2008
Posts: 3
L
learner Offline OP
New Member

Hi:

Base on CEC .

Does anybody know " What type enclosure box - 3R or 6P is right choice to used Under sprinkler " ?

Which rule?

thank you advance.

Leaner

Joined: Aug 2005
Posts: 265
S
Member
Rule 26-008 and Appendix B
Is the enclosure in an electrical room or vault?


Sixer

"Will it be cheaper if I drill the holes for you?"
Joined: Apr 2008
Posts: 3
L
learner Offline OP
New Member

Hi,sixer

Thank you.

the quiz not point out where is it.
from "Rule 26-008 and Appendix B" & table 65, I still can't make sure which type is right.

so could you please give more recommend?

Joined: Jan 2006
Posts: 60
R
Member
As per 2-400 and Table 65, type 4, or better, would be required.

Joined: Jun 2006
Posts: 613
M
Member
If the sprinkler is usually operating a type 4 is required. If it is for fire protection then any enclosure appropriate for the area without spriklers is ok. The normal use is what we determine the enclosure type not for a fire.

Now having said that there still are requirements for enclosures and equipment where a stream of water from a sprinkler head is required then 26-008 but that applies to the panels, transformers, switch boards etc.

A normal outlet box or JB where only wire and devices are installed would not require a special enclosure or every sprinled building would need to be completely wired per section 22.

In the case of a fire I presume we don't want the distrobution or transformers to fail from the sprikler putting water on the equipment. A fire pump or emergency lighting might be at stake. A wet location JB is overkill as this is a dry location except when a fire is present.

Joined: Apr 2008
Posts: 3
L
learner Offline OP
New Member

Thank you all.
because It's a quiz. the answer is type 3R or 6P only.
base on R26-008. I choice 3R. is it right?



Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Trumpy 11
Popular Topics(Views)
306,956 Are you busy
234,795 Re: Forum
219,134 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5