equipment ground/bond outside of conduit #176414
03/31/08 09:30 PM
03/31/08 09:30 PM
T
triple  Offline OP
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Is an equipment ground/bond wire ever allowed to run along the outside of the conduit containing the feed wires for distances exceeding six feet (whether new or as a supplement to an existing installation)? BTW, replacing an ungrounded receptacle with a grounded one does not apply to this situation.

Thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: equipment ground/bond outside of conduit [Re: triple] #176431
04/01/08 03:13 PM
04/01/08 03:13 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
Bonding jumpers can only be max 6' 250.102(E)

... but see what you make of 250.120(C)

Quote
(C) Equipment Grounding Conductors Smaller Than 6 AWG. Equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by a raceway or cable armor except where run in hollow spaces of walls or partitions, where not subject to physical damage, or where protected from physical damage.


... so you can run a ECG outside a raceway/cable if it is 6 or larger or otherwise protected from damage.

To be honest I have never seen it.


Greg Fretwell
Re: equipment ground/bond outside of conduit [Re: gfretwell] #176432
04/01/08 03:36 PM
04/01/08 03:36 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
I did see this discussed once in reference to adding grounds to a house that was ungrounded and it was surmised that you could run a bus of #6 through the crawlspace, attic or whatever was accessible and tap off #12 or #14 drops into the wall cavities to the boxes if the unprotected portion was very short, basically directly into the wall from the tap.

It seemed reasonable to me.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,837 Are you busy
184,197 Re: Forum
173,440 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.9518 MB (Peak: 1.0780 MB) Zlib enabled. Server Time: 2018-05-20 11:42:13 UTC