Receptacles above drop ceiling ? #175308
02/26/08 08:21 PM
02/26/08 08:21 PM
D
derater  Offline OP
Member
Joined: Mar 2002
Posts: 179
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks

Work Gear for Electricians and the Trades
Re: Receptacles above drop ceiling ? [Re: derater] #175309
02/26/08 09:35 PM
02/26/08 09:35 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by derater
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks


Yes absolutely receptacles are allowed above drop ceilings.

However you may not use them to feed a flexible cord, because 400.8 does not allow flexible cords above ceilings.

Low voltage transformers (wall warts) may be plugged directly into the receptacle if they are Class 2 devices and their output cord is not one of the NEC prohibited flexible cord styles. another use for these receptacles would be for portable/temporary equipment (i.e. work light)that is removed prior to "closing" the ceiling.

Re: Receptacles above drop ceiling ? [Re: JBD] #175347
02/27/08 10:56 AM
02/27/08 10:56 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 945
Chicago Illinois USA
As long as someone wants me to provide a receptacle above the ceiling for those purposes, I'm fine with it.
But as soon as they say that they want it to plug something into it and leave it (like a condensate return pump), I get antsy. I don't want to be part of their violation of 400.8; I wish that the Code was worded differently...it seems to be trying to fix one problem by addressing a different issue.


Ghost307

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,143 Are you busy
185,607 Re: Forum
174,943 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.004s) Memory: 0.9510 MB (Peak: 1.0769 MB) Zlib enabled. Server Time: 2018-07-20 20:27:51 UTC