#175308 - 02/26/08 08:21 PM Receptacles above drop ceiling ?  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks


Work Gear for Electricians and the Trades

#175309 - 02/26/08 09:35 PM Re: Receptacles above drop ceiling ? [Re: derater]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by derater
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks


Yes absolutely receptacles are allowed above drop ceilings.

However you may not use them to feed a flexible cord, because 400.8 does not allow flexible cords above ceilings.

Low voltage transformers (wall warts) may be plugged directly into the receptacle if they are Class 2 devices and their output cord is not one of the NEC prohibited flexible cord styles. another use for these receptacles would be for portable/temporary equipment (i.e. work light)that is removed prior to "closing" the ceiling.


#175347 - 02/27/08 10:56 AM Re: Receptacles above drop ceiling ? [Re: JBD]  
ghost307  Offline
Member
Joined: May 2005
Posts: 916
Chicago Illinois USA
As long as someone wants me to provide a receptacle above the ceiling for those purposes, I'm fine with it.
But as soon as they say that they want it to plug something into it and leave it (like a condensate return pump), I get antsy. I don't want to be part of their violation of 400.8; I wish that the Code was worded differently...it seems to be trying to fix one problem by addressing a different issue.


Ghost307


Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7524 MB (Peak: 0.8751 MB) Zlib enabled. Server Time: 2017-10-23 22:44:33 UTC