determing the load of heat pump compressors #1752 05/25/01 04:52 PM
Joined: May 2001
Posts: 36
C
C.Urch Offline OP
Member
How would one go about determining the load of a heat pump compressor in Volt Amperes? Is there a formula to convert tons to V.A.? Let's say that we have 3 - 3.5 ton units that has a R.L.A.(Running Load Amps) of 21.2, a minimum supply circuit of 28 amps, a max. fuse size of 45 amps and a minimum fuse of 35 amps. What would the load calculation or actual draw of these units be?

Work Gear for Electricians and the Trades
Re: determing the load of heat pump compressors #1753 05/25/01 06:00 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
test

Re: determing the load of heat pump compressors #1754 05/25/01 07:32 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Wouldn't you use the RLA figure?

Bill


Bill
Re: determing the load of heat pump compressors #1755 05/25/01 10:24 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
Why do you want the load in VA? It seems that you have all you need already. At the risk of going in circles--12,000 BTU/Hr. per ton. .293xBTU/hr.=watts. watts divided by (volts x power factor) or (volts x pf x 1.73 for 3phase)= amps. There is probably efficiency to consider also. I think this is right.

[This message has been edited by Redsy (edited 05-25-2001).]

Re: determing the load of heat pump compressors #1756 05/26/01 07:35 AM
Joined: May 2001
Posts: 36
C
C.Urch Offline OP
Member
In other words, one must "shoot from the hip" whether to upgrade a service from say 200 to 400 Amp when doing a re-model that is adding an additional heat and air system. If you think it will be close, then cover yourself. How about determing service size for new construction? Would it be safe to take the R.L.A. X 125% (for start up) per unit and and use this figure in determing your load calculation?

Re: determing the load of heat pump compressors #1757 05/28/01 09:32 AM
Joined: Oct 2000
Posts: 2,721
Scott35 Offline
Broom Pusher and
Member
Like Bill said, use the RLA [Running Load Amperes] to figure your KVA on each unit.

On large and/or multistage heatpumps, figure them to be LCLs [Long-Continuous Loads], so figure the RLA at 120% [or derate the circuit by 80% - but no need to do both]. If you know that they will not run for 3 hours + continuously, then LCL is not required. Heatpumps normally run at least 4 hours continuously at some time of the year, so best to figure LCL in your calcs.

List this on your Panel Schedule [with LCL added] for each heatpump.

List the heatpumps on a Load Calc as the NEC shows in the examples given at the end of the book, or in Article 220.

For LRA [Locked Rotor Amps], or starting amperes, there should be a rating on the nameplate stating what it should be calc'd at - but if that's not available, figure 600% of FLA for a somewhat close "Hip Shot"
Use the rated FLA of all motors per HP, not the RLA, when doing the 600% thingee.

Apply the LRA to your SCA [Short Circuit Amperes] calcs for motor contribution.

Sorry to throw so many TLA's at 'ya!!
[TLA = Three - Letter Acronyms].

Nothing like being bombarded with abbreviations!!


Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,060 Are you busy
205,042 Re: Forum
193,167 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3