#175044 02/20/08 03:09 PM
Joined: Mar 2003
Posts: 849
Y
Member
Total Load 3200 amps , Switch gear rated at 4000 amps

9 sets of 3-500 Kcmil & 1-4/0 neutral = 3420 amps.

Load 3200 Wire 3420 gear 4000 amps.

No main Six 800 amp switches

Legal per 230.80& 230.90 a EXCEPTION 3

READ PAGE 150 & 152 2005 NEC CODE HANDBOOK

Service Conductors Adquate for Load, Gear rated Above Load
Should be good to go Right.

Whatca say guys???
Yoopers

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Provided that your 3200 amp load is 125% of the continuous load plus 100% of the non-continuous load, I'd say OK.


Few things are harder to put up with than the annoyance of a good example.
Joined: Mar 2003
Posts: 849
Y
Member
That is the way it was Calculated.

Joined: Mar 2005
Posts: 399
A
Member
With six disconnects, and as calculated, it is Code compliant. Good to go. smile


Alan--
If it was easy, anyone could do it.