Section 409.60 of the 2005 NEC refers to "Multisection industrial control panels", but there is no definition. What would be an example of a Multisection industrial control panel? Would it be multiple sub-panels in a common enclosure?

Also, the second sentence of 409.60 seems ambiguous. Is a grounding bus required for a Multisection industrial control panel?

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding in Control Panels [Re: rwilsond] #174682
02/11/08 06:39 PM
02/11/08 06:39 PM
L
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
In a previous life, I used to be control panel assembler. On big assembly lines, we could have 6 Hoffman 4' wide by 6' tall enclosures bolted together to make 1 long-ass control cabinet. I think that would qualify as a "Multisection Industrial Control Panel."

Also look at multi-cabinet control consoles for control rooms at large industrial facilities, nuclear plants, etc.

Larry C

Re: Grounding in Control Panels [Re: LarryC] #174707
02/12/08 07:32 AM
02/12/08 07:32 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
I believe they're referring to large switchboard-style cabinets.

409.2 defines "Industrial control panel" and refers to pretty much anything, including breaker panels, switchgear, MCC, pushbuttons, etc. 409.60 just wants to make sure you properly bond them all together if they're installed as a single multisection unit. If you mount individual industrial control panels 1" apart, I do not believe 409.60 applies.

Edit: 409.2 was re-written in 2008, but doesn't appear to really change the definition, just presents it differently.

Last edited by SteveFehr; 02/12/08 07:33 AM.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,431 Are you busy
188,034 Re: Forum
177,615 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.005s) Memory: 0.9518 MB (Peak: 1.0789 MB) Zlib enabled. Server Time: 2018-10-19 16:11:38 UTC