New Member
Is flash PPE required inside the limited/restricted approach boundaries or not until the prohibited approach boundary is crossed? Can a visual inspection be done from the restricted zone without flash PPE?
Thanks, Mike

Horizontal Ad
MikeF #174313 02/01/08 06:13 PM
Joined: Mar 2005
Posts: 212
G
Member
This is one of the places where the NFPA 70E rules become very confusing. The boundaries you refer to are for SHOCK hazard, not flash hazard. Flash hazard and boundaries are calculated individually for the circumstance. The way it usually works out is that flash hazard PPE would be required within the shock hazard restricted/prohibited zones but not the limited zone. This is not always true however. Very high energy circumstances could extend the flash hazard areas well outside the shock hazard limited zone.

MikeF #174314 02/01/08 06:15 PM
Joined: May 2005
Posts: 984
Likes: 1
G
Member
PPE is needed in order to enter the limited/restricted zone.
Nothing will allow you to enter the prohibited zone and survive if there is an event.

You would need to de-energize the equipment (and make the prohibited zone go to zero) if you want to get that close to the equipment.


Ghost307
Joined: Feb 2008
Posts: 3
M
MikeF Offline OP
New Member
Definitely confusing....so SHOCK protection really amounts to rubber gloves, correct? FLASH protection is everything else? And if a flash approach boundary is determined to be at 4 feet, then all the other boundaries are pretty much out the window (?). Full protection from 4 feet in, in that situation?
Thanks so much!

MikeF #174379 02/03/08 11:01 AM
Joined: Sep 2005
Posts: 120
Z
Zog Offline
Member
Mike your answer is corrct assuming this is 600V or less we are talking about.

Ghost you seem to have the Arc Flash and Shock boundaries confused.

Greg, well put.

LAB may only be crossed by Qualified Personel (As defined in the 70E). RAB requires shock protection, usually just means gloves but can be more. PAB should be treated as the boundary you never cross but special training and hazard analysis would allow crossing. Shock boundaries only apply if there are exposed live parts.

Neither of these have anything to do with the arc flash boundary, the shock boundaries are dependant on voltage, the flash boundary has nothing to do with voltage levels, it is based on available fault current and clearing time of the protective device. PPE for flash protection must be worn any time you cross the Arc Flash boundary and "interact" with the equipment, weather the live parts are exposed or covered.


MV/HV Testing Specialist, "BKRMAN"

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Top Posters(30 Days)
Popular Topics(Views)
340,648 Are you busy
266,016 Re: Forum
246,937 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5