Hospital Feeders (Wireing Methods) #174132
01/27/08 11:33 AM
01/27/08 11:33 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
Critical, Life safety, Equipment, and normal.
Remember FEEDERS not branch circuits.
Rubber covered MC Cable???? .Single phase 2 hots , neutal, ground.

2017 / 2014 NEC & Related Books and Study Guides
Re: Hospital Feeders (Wireing Methods) [Re: Yoopersup] #174133
01/27/08 12:07 PM
01/27/08 12:07 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Yoop, Code quiz?

Not sure what your asking.

Re: Hospital Feeders (Wireing Methods) [Re: leland] #174157
01/28/08 01:26 AM
01/28/08 01:26 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
Question is. Is there any problem using rubber covered MC for hospital feeders??

Re: Hospital Feeders (Wireing Methods) [Re: Yoopersup] #174199
01/29/08 12:12 AM
01/29/08 12:12 AM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
I see nothing to prevent it.
Appears that the critical items come in to play at the branch ckt level.

Re: Hospital Feeders (Wireing Methods) [Re: leland] #174222
01/29/08 06:50 PM
01/29/08 06:50 PM
W
WireNuts29  Offline
Member
Joined: Jul 2007
Posts: 85
Mass, U.S.A.
From past experience, as a helper at the time. If I can recall correctly you need the 2 hour burn on all critical feeders.Which seems to me in a hospital all patient care areas. I remember using M.I cable for this a few tears back. I'd have to check my code book for the article numbers, thisis just off the top of my head. Also seems to me most hospitals I've done work in have panels dedicated to critical loads, usually having generator back up.

Re: Hospital Feeders (Wireing Methods) [Re: WireNuts29] #174241
01/30/08 01:02 AM
01/30/08 01:02 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
Yer thinking of Fire Pumps . Hospital feeders two hr fire rateing I don't think so.

Re: Hospital Feeders (Wireing Methods) [Re: Yoopersup] #174268
01/30/08 08:35 PM
01/30/08 08:35 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
In Ma. We have the 2 hr rateing for feedrs.
However, Some inspectors have trouble diferentiating feedrs from branch ckts.

Re: Hospital Feeders (Wireing Methods) [Re: leland] #174278
01/31/08 12:08 AM
01/31/08 12:08 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 845
Michigan
Doesn't Ma. use only the NEC?? I carried a Ma. License for yrs and took the test (Masters) in 1999 . I don't remember any additions to the NEC at that time.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Tom
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,623 Are you busy
186,362 Re: Forum
175,828 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.028s Queries: 15 (0.005s) Memory: 0.9920 MB (Peak: 1.1565 MB) Zlib enabled. Server Time: 2018-08-19 09:42:07 UTC