Critical, Life safety, Equipment, and normal.
Remember FEEDERS not branch circuits.
Rubber covered MC Cable???? .Single phase 2 hots , neutal, ground.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Aug 2007
Posts: 853
L
Member
Yoop, Code quiz?

Not sure what your asking.

Joined: Mar 2003
Posts: 849
Y
Member
Question is. Is there any problem using rubber covered MC for hospital feeders??

Joined: Aug 2007
Posts: 853
L
Member
I see nothing to prevent it.
Appears that the critical items come in to play at the branch ckt level.

Joined: Jul 2007
Posts: 85
W
Member
From past experience, as a helper at the time. If I can recall correctly you need the 2 hour burn on all critical feeders.Which seems to me in a hospital all patient care areas. I remember using M.I cable for this a few tears back. I'd have to check my code book for the article numbers, thisis just off the top of my head. Also seems to me most hospitals I've done work in have panels dedicated to critical loads, usually having generator back up.

Joined: Mar 2003
Posts: 849
Y
Member
Yer thinking of Fire Pumps . Hospital feeders two hr fire rateing I don't think so.

Joined: Aug 2007
Posts: 853
L
Member
In Ma. We have the 2 hr rateing for feedrs.
However, Some inspectors have trouble diferentiating feedrs from branch ckts.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Mar 2003
Posts: 849
Y
Member
Doesn't Ma. use only the NEC?? I carried a Ma. License for yrs and took the test (Masters) in 1999 . I don't remember any additions to the NEC at that time.