Headroom for panel?
#173415
01/09/08 02:43 PM
|
Joined: Jan 2005
Posts: 109
OP
Member
|
I have a customer who wants to move (replace) his panel from an upstairs closet to the basement, and add a generator transfer switch.
Basement headroom is only 5', and I seem to remember a minimum height requirement from somewhere, but can't seem to put my finger on it.....
Anybody recall, or am I dreaming?
Thanks, Grov
|
|
|
Re: Headroom for panel?
[Re: Grover]
#173424
01/09/08 04:28 PM
|
Joined: Nov 2007
Posts: 763
Member
|
Grover, If it's a dwelling and 200 Amps or less, then 110.26[E], exception, should give you the green light.
|
|
|
Re: Headroom for panel?
[Re: KJay]
#173459
01/10/08 07:52 AM
|
Joined: Jan 2005
Posts: 109
OP
Member
|
Bingo! Thanks KJay - I remembered the section, but not the exception.
Thanks!
Grov
|
|
|
|
|