Re: A Big problem at The County Shop [Re: wire_twister] #172824 12/27/07 05:28 PM
Joined: Mar 2007
Posts: 49
A
ausador Offline
Member
jdevlin he specifically said in his first post that the service was strictly 120/208volt 3 phase. Also a 600volt service would still not explain the 255volts seen at the fixtures. He is missing some element here and consequently so are we, hopefully he will let us know what it is.....

Work Gear for Electricians and the Trades
Re: A Big problem at The County Shop [Re: ausador] #172827 12/27/07 07:32 PM
Joined: Apr 2007
Posts: 33
R
RDK Offline OP
Member
Found the problem. The last guy who got fired installed a transformer up in the attic. Ill try to post some pix latter this week. THis was the same guy who installed a pannel over top of someone's crapper. Ill also post pix of that. Thanks to all. Now all the lights work

Re: A Big problem at The County Shop [Re: RDK] #172845 12/27/07 11:21 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
RDK,
So then, the 28 lights were Metal Halide fixtures with a single, large VA, multi-circuit transformer?
Can’t say that I have ever seen a transformer like that before.



Re: A Big problem at The County Shop [Re: RDK] #172847 12/28/07 12:10 AM
Joined: Nov 2005
Posts: 141
C
Check Pilot Offline
Member
I see a broken neutral. Start at the service FROM the meter IN the panel and measure the volts from each side to ground or the EGC - not the neutral. If it's anything but 120 volts - high, or low for that matter, the neutral is broken somewhere before the panel, - maybe the meter perhaps? Then measure the voltage in the panel from neutral to the ground or EGC connection. Voltage from neutral to ground of anything over about 2 volts indicates a busted neutral somewhere. Hope that helps you.

Page 3 of 3 1 2 3

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 12
dsk 6
Popular Topics(Views)
262,457 Are you busy
197,593 Re: Forum
186,600 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3