Trick440,
From what I can gather from the downloaded instruction manual, it looks like that Ideal unit may only be good for single phase, maybe even only an individual branch circuit. I think you would need to be able to monitor all phases at once to get an accurate account of what is happening in a commercial setting.
I have been looking around for a new PQ meter myself and so far, the one that offers the most features and bang for the buck is the Extech 382090.
At $1995.00 it is full featured, can log up to 20,000 readings, shows PF and 1-27 harmonics. It also comes complete with four current clamps for true 3-phase monitoring, a set of standard alligator test leads, carrying case, batteries and software for downloading data to your computer. The software is an important item, because you really have to be able to print out and show the test results to the customer. Especially if you are going to make recommendations for expensive changes to be made.
All the new Fluke units I have looked at are well over $4000.00. That is just too much for a small company to purchase just for occasional use. I think this may be why many electrical contractors leave this type of work to others who specialize in the PQ field.
Regards