Shunt Trip Breaker Wiring #171919 12/08/07 08:42 PM
Joined: Sep 2004
Posts: 174
B
bot540 Offline OP
Member
I need to install a few shunt trip Square D QOB breakers and was wondering how exactly are these things are wired. Off the ansul system I have three wires yellow, brown, and blue. I believe that the yellow is the common and the blue is the normally closed contact, which make the brown the normally open contact.
I am assuming you hook the breaker up to the normally open contact. Is this correct?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Work Gear for Electricians and the Trades
Re: Shunt Trip Breaker Wiring [Re: bot540] #171927 12/08/07 10:36 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
Yellow should be common,brown N/O.
Dedicate a ckt from a NON-shunted panel to this contact. then to the ST brkr/brkrs.On activation the relay closes and shunts the brkr. Panel down.
The exhaust fan/s should not be shunted on deployment.

Re: Shunt Trip Breaker Wiring [Re: leland] #171931 12/08/07 10:59 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
====The exhaust fan/s should not be shunted on deployment. ==

I'll retract this, untill I can quote the art.
It is common practice, I just can't find it rght now.

Re: Shunt Trip Breaker Wiring [Re: leland] #171933 12/08/07 11:24 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member

NFPA-17A-
4.4.3.5-- Exhaust fans do not need to be shut down on deployment of the wet system.


But in 5.6.2.2- all fuel and heat sources MUST be shut down.
easy to shunt trip the panel.
4.4.3.4- solid fuel- needs no shut down.Fancy Pizza joint--(Joint mmmm)
4.4.3.7- requires all shut down devices need a manual reset.
shunt trip brkr, coverd.

Re: Shunt Trip Breaker Wiring [Re: bot540] #171940 12/09/07 06:47 AM
Joined: Sep 2004
Posts: 174
B
bot540 Offline OP
Member
So the breaker needs a 120 volt signal to trip?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Re: Shunt Trip Breaker Wiring [Re: bot540] #171941 12/09/07 07:51 AM
Joined: Jul 2002
Posts: 680
W
walrus Offline
Member
The shunt trips I've wired need 120v signal to trip

Re: Shunt Trip Breaker Wiring [Re: walrus] #171944 12/09/07 08:26 AM
Joined: Dec 2000
Posts: 4,281
electure Offline
Member
I much prefer using a contactor instead of shunt trip breakers.
They don't take up valuable space in the panel (shunt trips take an extra pole space for the trip), and are more economical.

Re: Shunt Trip Breaker Wiring [Re: electure] #171945 12/09/07 09:12 AM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
Agree, if you only have a few peices of equipment to shut down, contactor may be more economic.
Most gas equip. will have a mechanicle gas valve shut off.

Only the equipment in the protected area (hazard) needs to be dumped. Check your local codes and follow specs.

Last edited by leland; 12/09/07 09:13 AM.
Re: Shunt Trip Breaker Wiring [Re: walrus] #171947 12/09/07 10:00 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
Originally Posted by walrus
The shunt trips I've wired need 120v signal to trip
I've seen some with 24VDC and 48VDC shunt trip- you'd need to check the specs on the breaker as to what it needs.

Should be OK to feed shunt-trip from this panel. After all, it will have power TO shunt trip, and after shunt trip... you don't really need power anymore!

Also, you might want to note somewhere on the panel that it's configured to shunt trip. We had one go off once over lunch when a contractor working sprinklers in another part of the building opened a valve just outside a data center to bleed the system and a flow sensor shunt-tripped the main breaker and killed power to the data center. DOH! None of the ITs had any clue what had happened or how to recover, and were running around trying to figure out why the generator hadn't started. - NOTHING was labeled, neither the panel nor the sprinkler. It's labeled now.

Last edited by SteveFehr; 12/09/07 10:06 AM.
Re: Shunt Trip Breaker Wiring [Re: SteveFehr] #171948 12/09/07 10:43 AM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
I've done that! Wow,they don't like it much.
Coz everybody looses 10, mil$ a minute. Just ask them.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
NORCAL 1
Popular Topics(Views)
261,237 Are you busy
196,400 Re: Forum
185,672 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3