Secondary conductor size for transformers #171772 12/05/07 09:41 AM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
Hello, can someone tell me the rule for sizing secondary conductors of a dry type transformer. I know it is 125% minimum, but what rule is it when you do not have secondary protection and you are sizing your panel board based on
14-606(2)
Thanks


Never trust an electrician with no eyebrows!!
Tools for Electricians:
Re: Secondary conductor size for transformers [Re: mr_electrician] #171773 12/05/07 10:03 AM
Joined: Jan 2006
Posts: 60
R
Rick Kelly Offline
Member
14-100(d) comes to mind...

Re: Secondary conductor size for transformers [Re: mr_electrician] #171780 12/05/07 04:07 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
I think you have it covered there, 26-256 for the 125%, but that is maximum, not minimum.

Re: Secondary conductor size for transformers [Re: jay8] #171783 12/05/07 04:53 PM
Joined: Nov 2001
Posts: 45
B
bill woods Offline
Member
Doesn't 26-256 cover overcurrent protection? Aren't we talking about conductor size here? Shouldn't we be looking at 26-258? If you install overcurrent devices in the primaries, and these devices limit the current on the secondaries to an amperage less than the KVA rating of the transformer allows don't you size the secondary conductors to this value?

Re: Secondary conductor size for transformers [Re: bill woods] #171785 12/05/07 06:13 PM
Joined: Jan 2006
Posts: 60
R
Rick Kelly Offline
Member
I take back my earlier mention of 14-100(d) for the following reason.

14-100(d) can not apply as its subrule (ii) requires that the circuit teminate at a single overcurrent device, which in this case we do not have.

So it looks like...

As per rule 26-258(2a) the minimum ampacity of the secondary conductors must be sized at 125% of the transformer's rated secondary current.

Good catch Bill, your comment made me rethink this.

Re: Secondary conductor size for transformers [Re: Rick Kelly] #171814 12/06/07 12:08 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
Yes, oops, I read that as overcurrent when the post mentioned not using secondary protection, so that would be 125% minimum on conductor size.
But Bill, the wording on 26-256 refers to rated current of the transformer, so you wouldnt limit current on the secondary conductors to less than the KVA rating of the transformer unless you wanted to do so, since 125% is the maximum, you could go less if you chose to.

Re: Secondary conductor size for transformers [Re: mr_electrician] #171859 12/07/07 08:21 AM
Joined: Jun 2007
Posts: 106
M
mr_electrician Offline OP
Member
Thanks guys for taking the time on this subject. I was talking with the local inspector and he said it like this....125% of full load current on the secondary when there is no protection on the secondary (what rule is that?). So even when your choking transformers you would size your secondary conductors based on 14-100(f)(ii) and multiply by 125%
Example: A 45KVA can put out 115 amps when the primary is fused at 40Amps. Now if I were to choke the transformer and fuse the primary at 30Amps, then the secondary conductors would be sized for 108A (30 X 2.88 X 1.25 = 108)
Clear as mud!


Never trust an electrician with no eyebrows!!

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
BigB 4
Popular Topics(Views)
266,188 Are you busy
201,019 Re: Forum
189,707 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3