ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 4
Recent Posts
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
Bathroom electrical
by gfretwell. 08/14/17 02:05 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,863 Are you busy
175,421 Re: Forum
167,715 Need opinion
Who's Online Now
1 registered members (cableguy619), 37 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#171772 - 12/05/07 09:41 AM Secondary conductor size for transformers  
mr_electrician  Offline
Member
Joined: Jun 2007
Posts: 106
London, Ontario
Hello, can someone tell me the rule for sizing secondary conductors of a dry type transformer. I know it is 125% minimum, but what rule is it when you do not have secondary protection and you are sizing your panel board based on
14-606(2)
Thanks


Never trust an electrician with no eyebrows!!

Tools for Electricians:

#171773 - 12/05/07 10:03 AM Re: Secondary conductor size for transformers [Re: mr_electrician]  
Rick Kelly  Offline
Member
Joined: Jan 2006
Posts: 60
Iqaluit, NU, Canada
14-100(d) comes to mind...


#171780 - 12/05/07 04:07 PM Re: Secondary conductor size for transformers [Re: mr_electrician]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I think you have it covered there, 26-256 for the 125%, but that is maximum, not minimum.


#171783 - 12/05/07 04:53 PM Re: Secondary conductor size for transformers [Re: jay8]  
bill woods  Offline
Member
Joined: Nov 2001
Posts: 45
Doesn't 26-256 cover overcurrent protection? Aren't we talking about conductor size here? Shouldn't we be looking at 26-258? If you install overcurrent devices in the primaries, and these devices limit the current on the secondaries to an amperage less than the KVA rating of the transformer allows don't you size the secondary conductors to this value?


#171785 - 12/05/07 06:13 PM Re: Secondary conductor size for transformers [Re: bill woods]  
Rick Kelly  Offline
Member
Joined: Jan 2006
Posts: 60
Iqaluit, NU, Canada
I take back my earlier mention of 14-100(d) for the following reason.

14-100(d) can not apply as its subrule (ii) requires that the circuit teminate at a single overcurrent device, which in this case we do not have.

So it looks like...

As per rule 26-258(2a) the minimum ampacity of the secondary conductors must be sized at 125% of the transformer's rated secondary current.

Good catch Bill, your comment made me rethink this.


#171814 - 12/06/07 12:08 PM Re: Secondary conductor size for transformers [Re: Rick Kelly]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
Yes, oops, I read that as overcurrent when the post mentioned not using secondary protection, so that would be 125% minimum on conductor size.
But Bill, the wording on 26-256 refers to rated current of the transformer, so you wouldnt limit current on the secondary conductors to less than the KVA rating of the transformer unless you wanted to do so, since 125% is the maximum, you could go less if you chose to.


#171859 - 12/07/07 08:21 AM Re: Secondary conductor size for transformers [Re: mr_electrician]  
mr_electrician  Offline
Member
Joined: Jun 2007
Posts: 106
London, Ontario
Thanks guys for taking the time on this subject. I was talking with the local inspector and he said it like this....125% of full load current on the secondary when there is no protection on the secondary (what rule is that?). So even when your choking transformers you would size your secondary conductors based on 14-100(f)(ii) and multiply by 125%
Example: A 45KVA can put out 115 amps when the primary is fused at 40Amps. Now if I were to choke the transformer and fuse the primary at 30Amps, then the secondary conductors would be sized for 108A (30 X 2.88 X 1.25 = 108)
Clear as mud!


Never trust an electrician with no eyebrows!!


Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7857 MB (Peak: 0.9388 MB) Zlib enabled. Server Time: 2017-08-17 03:49:40 UTC