ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 220 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: May 2005
Posts: 41
L
Member
One more question. If a manufacturer is selling a series rated system, should they indicate where the series rating takes place to accomplish this AIC correction? And what assurance is there that they are providing an integrated and effective system?
Thanks all.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2006
Posts: 613
M
Member
Last leg
I think now that Dave is back on subject the answer lies in his last reply. In Series rating there is NO coordination except accidentally. The right breaker might ultimately trip alone but it is completely possible and part of the design that both the branch and main breakers will trip.
If you want coordinated tripping there are some simpler methods and complex methods to achieve coordination. For me coordination means the O/C device closest to the fault is the only one that trips. It is easiest to achieve in fuses and electronic controlled breakers. Thermal magnetic breakers can be coordinated but as Dave said it is a little less reliable than a more sophisticated electronic trip control breaker.
If the load is really critical don't go for series rated gear.
Coordination is a very complex subject and is an absolute necessity in some factories never mind hospitals data centers, etc.

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by Last Leg
One more question. If a manufacturer is selling a series rated system, should they indicate where the series rating takes place to accomplish this AIC correction? And what assurance is there that they are providing an integrated and effective system?
Thanks all.


It is up to the designer, not the manufacturer, to decide when and if series rated equipment is acceptable in their system. For example if selective coordination is absolutely required then I would probably not accept series ratings, however for a general purpose lighting/receptacle panel I would accept them.

Joined: May 2004
Posts: 116
S
Member
Last Leg;

Go to: "http://www.bussmann.com/" and look under their literature and technical information areas for information.

If you like, send me a private email (let me know you are from the ECN forum) and I can email you several files that I have about Series Rating.

Steve


Thanks
Steve
Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5