ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Old Fused Panel
 Old Fused Panel

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 20 guests, and 35 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Joined: Oct 2000
Posts: 3,684
Likes: 4
Admin Offline OP
Administrator
Member
Quote
Attached are several code violations all for the same job. I was called out to “finish” the little bit of stuff that was left by the other contractor. When I told the property manager that we would have to redo pretty much the entire installation he sounded surprised.

The pictures should speak for themselves, there are so many code violations in each of them it is hard to encapsulate in the captioning. All of the new looking items were installed by the other electrician. I was trying to get a name from them so I could turn them in to the Contractors Board.

Roger Ervine

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

[Linked Image from electrical-photos.com]

Horizontal Ad
Joined: Jan 2005
Posts: 5,474
Likes: 3
Cat Servant
Member
Looks like a 'work in progress' ... one that was stopped before serious harm was done!

FWIW, here the PoCo would not let us use PVC pipe for an overhead feed.

I am puzzled by the extended time that the job is taking ... as suggested by the pictures. A job like this has but one way to do it - and that is, to kill all the power for the two or three days needed, and GET IT DONE. I've done such in sub-zero weather ... using a 'spider box' to keep the heat on and the fridge running.

Joined: Mar 2004
Posts: 391
B
Member
In picture 6 that shows the PVC pipe running along the side of the house, what's the violation there? Is it that they went to the trouble to install their new entrance conductors over-top the old ones that should be getting demo'd? Or that they put their strut at an elbow?

And I haven't worked on many residential services, so I don't understand the violation in picture 7 either. I don't even understand the label: A 125A meter socket rated for 400 amps...? Is that 400 total and 125 per meter or something?

The rest of that, however, is obviously pretty nasty. It always rings alarm bells for me when I hear stories about electricians being called to "just finish a little bit" of someone else's work. There's usually a good reason that "someone else" isn't there anymore. Either they were fired for hack work or skipped out to avoid prosecution for hack work.

-John

Joined: Jan 2007
Posts: 6
F
Junior Member
Originally Posted by BigJohn
In picture 6 that shows the PVC pipe running along the side of the house, what's the violation there? Is it that they went to the trouble to install their new entrance conductors over-top the old ones that should be getting demo'd? Or that they put their strut at an elbow?

And I haven't worked on many residential services, so I don't understand the violation in picture 7 either. I don't even understand the label: A 125A meter socket rated for 400 amps...? Is that 400 total and 125 per meter or something?

The rest of that, however, is obviously pretty nasty. It always rings alarm bells for me when I hear stories about electricians being called to "just finish a little bit" of someone else's work. There's usually a good reason that "someone else" isn't there anymore. Either they were fired for hack work or skipped out to avoid prosecution for hack work.

-John


Picture 6 shows a 2" conduit running to the 4 meter stack. The nameplate picture is for the four meter main buss (400A). By my calculations Table 310.15(B)(6) 400A copper is 400kcmil wire or a minimum 3 conductor feeder conduit size of 3" for the conduit(they used 2"). The conduit is coming from the junction box on the corner that is a nema 3R can mounted upside down. I am pretty sure without even checking that the can dimension is WAY undersized for that size wire, I would guess somewhere around a 24X24X6 without doing the calculation. One of the other pictures shows exposed PVC conduit running through the utilities gas piping which is a big no-no. As far as the PVC being legal overhead I don't think that is even allowed. I personally would have installed EMT or rigid for the installation.

Last edited by Fidelity Electric; 12/03/07 12:56 AM.

You can learn a lot from a dummy...buckle up!!
Joined: Feb 2004
Posts: 1,438
Member
This place reminds me so much of A Few Things That Blew My Fuse , it's not even funny.... Ironically also from when I was working in San Diego. (Old Town) Even worse, this looks like some shotgun little cottages that I remember taking a look at someplace around University/Euclid Ave. area... I walked away from that one, then drove away alot faster!

Randy

Joined: Jul 2002
Posts: 680
W
Member
They taped the wire nuts, what else can you ask for smile

Was some of that temporary?? while they completed the job??

Joined: Jul 2007
Posts: 85
W
Member
I want to see an over all pic of the entire wall. This is quite a bit of hackermanship. It's a shame cause thats not a cheap meterstack. apparently they forgot to pick up the how to change a service 1-2-3 book at home depot.

Horizontal Ad
Joined: Jun 2007
Posts: 50
H
Member
Wow....just wow! That's about all I can say for this fine example of how not to do it.

Did they actually expect this to pass?

Joined: Aug 2005
Posts: 214
E
Member
I have a problem with the opside-down 3R can, and BIG problems with the way they made up the temp

What I do not have a problem with is the size of the pipe in relation to the meter pack, the proper way to do this would be to perform a load calc on the building, and feed the meter pack based on that. It looks like they're missing a clamp on that PVC right near the 90 because the conduit both has to be on top of that gas line, and to get the proper depth for the meter pack, I would have used deep channel strut to avoid both of these issues.

my $0.02
-Will

Joined: Jul 2007
Posts: 265
W
Member
A 400 amp meter set needs a feeder capable of 400 amps. We can not control what someone might do in the future, therefore if it says 400 on the plate it should be able to carry it.


Jimmy

Life is tough, Life is tougher when you are stupid
Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
327,838 Are you busy
252,691 Re: Forum
235,318 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5