Hi,
Under the 2002 code is there a requirment for the ups to be able to disconnect commercial power if there is a fire?

If so what article?

Thanks

Windy


We all live under one King
Horizontal Ad
Joined: Jul 2007
Posts: 1,337
S
Member
645.11


"Live Awesome!" - Kevin Carosa
Joined: Mar 2005
Posts: 1,213
S
Member
Remote EPO is only required for datacenters. For all other appliations, no remote is required, though certainly not prohibited. (Try convincing people that they need a magic "off" button without a code to point to, though!)