Marine Shipboard wiring #171386 11/27/07 12:51 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
I have been looking for the history of switching the neutral at each breaker. Although in most cases, it is not required per IEEE 45, USCG Title 45, and ABS just to name a few, I come across this in older steel vessels. I think it is a relic from the ol' ungrounded days. This would explain I see this in older ships that have been since retrofitted with grounded systems but kept the origional distribution system due to the expense. Can anyone shed actual knowledge on the history?


"Live Awesome!" - Kevin Carosa
Work Gear for Electricians and the Trades
Re: Marine Shipboard wiring [Re: sparkyinak] #171394 11/27/07 06:58 AM
Joined: Mar 2005
Posts: 1,213
S
SteveFehr Offline
Member
Naval ships don't use neutrals, but use 110/63V floating delta, where both terminals in receptacles are hot. The only time the neutral terminals are actually grounded is when fed via isolation transformers or isolated UPS, but that's restricted to very particular applications and done at the equipment, not the panel. This method of distribution lowers the voltage potential (which is important when considering damage control while flooded with saltwater) and increases fault tolerance- you can short out a phase to ground and the system will still work. There are, of course, no ground wires, just bonding to the ship's hull.

So, what you see are 3-phase panels with all "1-phase" circuits fed from 2-pole breakers and ungrounded cables.

Last edited by SteveFehr; 11/27/07 06:59 AM.
Re: Marine Shipboard wiring [Re: SteveFehr] #171401 11/27/07 10:55 AM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
They also have 440 delta for the bigger loads.


Greg Fretwell
Re: Marine Shipboard wiring [Re: gfretwell] #171415 11/27/07 05:20 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline OP
Member
I am not talking about navel ships but other steel marine vessels. Their AC systems are required to be grounded. Most of the older steel vessels I have encountered are breaking the nuetral at the breaker. All applicable standards state that this is optional, not a requirement. I understand in general why the Navy does what it does but it is not applicable to civilian application


"Live Awesome!" - Kevin Carosa

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,469 Are you busy
209,379 Re: Forum
196,651 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3