#12 THHN in 3/4" conduit. #170844
11/13/07 06:02 PM
11/13/07 06:02 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
How are most guys doing this? What I'm hearing is only pull 3 #12 curcuits in 3/4" conduit. Is this what most guys are doing?

Please correct my math. If I pulled more, say 9 current carrying #12 conductors. Than it would be 2400w, derated to 1680w. So I could load the circuit up to 1680w.. (taking into consideration continuous loads)

I would like to know what most guys are doing. My background is residential, commercial is a different animal I'm still trying to grasp.

Thanks.


Shake n Bake
Work Gear for Electricians and the Trades
Re: #12 THHN in 3/4" conduit. [Re: Trick440] #170846
11/13/07 07:05 PM
11/13/07 07:05 PM
T
Trick440  Offline OP
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
I did a search and figured it out.

9 current carrying conductors, neutrals count as current carrying.. Would keep #12 rated for 20amps. So 4 circuits in a 3/4"


Shake n Bake
Re: #12 THHN in 3/4" conduit. [Re: Trick440] #170850
11/13/07 09:02 PM
11/13/07 09:02 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,365
Estero,Fl,usa
You could put 4 multiwire single phase circuits in a conduit. That looks like 8 circuits at 120v.
310.15(B)(4)(a)
If you didn't have any harmonic loads it could be 3 3p wye multiwires for 9 120v circuits.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Khombo 2
Popular Topics(Views)
255,771 Are you busy
191,751 Re: Forum
181,510 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 15 (0.004s) Memory: 0.9514 MB (Peak: 1.0776 MB) Zlib enabled. Server Time: 2019-06-20 19:25:18 UTC