#170818 11/12/07 07:13 PM
Joined: Oct 2000
Posts: 3,666
Likes: 1
Admin Offline OP
Administrator
Member
Quote
This is what happens when the expansion fitting is NOT installed. The side of the box was pulled completely out. These were taken in a parking garage that is being renovated. The metal conduit will probably be replaced by rigid non-metallic conduit sched. 80 WITH expansion fittings.

[Linked Image from electrical-photos.com]

Quote
This is the second of two pictures showing an expansion fitting on rigid conduit. This is how it should be done.

Alan Nadon

[Linked Image from electrical-photos.com]

2017 / 2014 NEC & Related Books and Study Guides
Joined: Mar 2004
Posts: 391
B
Member
I understand the reason for expansion fittings, but never really saw an install where I was thinking "They'd really be up a creek if they hadn't put that expansion coupling in." Now here's a dramatic example of what happens when you don't. Neat.

-John

Joined: Oct 2007
Posts: 56
S
Member
Wow.

Is expansion/contraction really what caused that?? I never would have guessed that a lack of provision for expansion could result in something this dramatic.

Kinda makes me ponder the 250 feet or so of EMT I just ran the other day...oh wait, that was inside a heated building. *whew*


Shawn.

Joined: Aug 2002
Posts: 402
J
Member
That must have been some long conduit run to expand/shrink what looks like 2 inches. Are you sure it is not from damage further down the conduit run?

Joined: Feb 2004
Posts: 1,437
Member
There's a run of 3/4 galvanized that runs along a fenceline for about 1200 feet out where I work (For H2S monitors) In the cold, it's straight as an arrow, but once it gets above about 80F or so... It starts doing the wave... along the WHOLE run!

Joined: Mar 2005
Posts: 1,213
S
Member
The coefficient of thermal expansion for steel is 0.00000645in/in/deg. Doesn't sound like much, but for a 100' piece of pipe, the difference between a -20F day and a 110F day is 1". Aluminum expands twice as much as steel. Concrete is practically identical to steel. (Convenient for rebar, eh?) BUT, if that concrete has expansion joints, and the steel doesn't...

PVC is far worse, as it has a much higher coefficient of expansion. A similar piece of RNC would have an appx 4.5" expansion/contraction.

Last edited by SteveFehr; 11/20/07 01:45 PM.
Joined: Mar 2008
Posts: 144
Member
look @ how bent up it is, i don't think an expansion fitting would of helped that


-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,982 Are you busy
216,728 Re: Forum
203,148 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5