#170663 - 11/08/07 01:00 PM Submersible well pump disconnect location  
tark52  Offline
New Member
Joined: Nov 2007
Posts: 1
TN
I'm installing a sub. pump, 240 volt 2-wire that pumps 250' to my pressure tank under the house. Where does the code require the disconnect to be located? Can I locate it under the house?


2017 / 2014 NEC & Related Books and Study Guides

#170665 - 11/08/07 02:21 PM Re: Submersible well pump disconnect location [Re: tark52]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,116
Estero,Fl,usa
430.102 says "The disconnecting means shall be located in sight from the controller location".
In the case of most submersible pumps the controller is the pressure switch. If you have the disconnect there I think you have fulfilled the requirement. You could also use a locking switch somewhere else with proper labelling. (using exception 1)


Greg Fretwell

#170669 - 11/08/07 03:50 PM Re: Submersible well pump disconnect location [Re: gfretwell]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Greg- I agree with you and this might be one of those place that qualifies under 430.102(B) Exception (a) in which case if the pump were submersed it would be impracticable to install a disconnect switch at the motor.


George Little

#170697 - 11/09/07 12:05 AM Re: Submersible well pump disconnect location [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,116
Estero,Fl,usa
From a practical sense from someone who has lived with a well for the last quarter century, the pressure switch is the first place a person will go to try to fix this thing and that is the best place for the disconnect. Having one down in the well is impractical although I assume someone might want one at the well head. The problem is, unless you have a separate box for the disconnect and the wires feeding the well, it is a distinction without a difference since the line side of the disconnect might still be available to the repairer.

As an OT aside, I finally gave up on screwing with well pressure switches and I put mine on an Amp plug with a Hansen quick disconnect water connection. I keep a "hot spare" so when I am out there in my skivvies at 2 AM I can just swap it out.
I also built a "house" for my well equipment that keeps it out of the weather but I guess "freezing" keeps yours inside. In Florida carpenter ants are the biggest enemy of pump switches. It seems to be a perfect home for them


Greg Fretwell


Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.7619 MB (Peak: 0.8944 MB) Zlib enabled. Server Time: 2017-09-23 03:58:06 UTC