wire size #170486
11/04/07 11:14 AM
11/04/07 11:14 AM
D
drkana  Offline OP
New Member
Joined: Nov 2007
Posts: 4
illinois usa
what size wire in paralell is equal to 300 mcm and is there a reference table somwhere?

Tools for Electricians:
Re: wire size [Re: drkana] #170491
11/04/07 12:57 PM
11/04/07 12:57 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
See Table 8 in Chapter 9

Roger

Re: wire size [Re: drkana] #170515
11/04/07 10:29 PM
11/04/07 10:29 PM
D
drkana  Offline OP
New Member
Joined: Nov 2007
Posts: 4
illinois usa
looking at that table it looks like 3/0 or 2/0 but i'm not sure any suggestions.

Re: wire size [Re: drkana] #170564
11/05/07 10:22 PM
11/05/07 10:22 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
What are you trying to do?
Don


Don(resqcapt19)
Re: wire size [Re: resqcapt19] #170567
11/06/07 07:22 AM
11/06/07 07:22 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
2/0 won't make it but, I think Don's question needs to be answered, it may save you some grief.

Roger

Re: wire size [Re: Roger] #170615
11/07/07 08:30 AM
11/07/07 08:30 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
With alternating current, magnetic fields build up inside the cable and skin resistance comes into play, so cable ampacity doesn't scale linearly with cross-section. In addition, cooling is related to the surface area of the cable, and larger cables have less surface area than two smaller ones to dissipate heat. Ergo, you can safely (and legally) carry more current through 2x 150MCM than through 1x 300MCM, and 2x 1/0 may be sufficient depending on what you intend.

If you're talking DC, reference Chapter 9, Table 8. If you're talking 60Hz AC, reference a combination of 310.60 with the derating rules of 310.1(B)(2)(a)... and the myraid of other codes that may apply.

Last edited by SteveFehr; 11/07/07 08:33 AM.
Re: wire size [Re: SteveFehr] #171088
11/19/07 03:50 PM
11/19/07 03:50 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
Table 310.16 takes all of this into consideration. Assuming THWN insulated copper conductors, 300 kcmil has an ampacity of 285 amps, therefore 2 paralleled 1/0 AWG conductors in separate conduit or cable would have equivalent current carrying capacity. It is necessary to keep these paralleled conductors in separate conduit or cables because of the heat buildup when more than 3 current carrying conductors are installed in one conduit (300.15(B)(2)(a))


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Popular Topics(Views)
255,753 Are you busy
191,721 Re: Forum
181,492 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 0.9839 MB (Peak: 1.1418 MB) Zlib enabled. Server Time: 2019-06-19 12:59:35 UTC