Panel enclosure as raceway #170261
10/30/07 02:57 PM
10/30/07 02:57 PM
B
bman  Offline OP
Member
Joined: Jul 2006
Posts: 20
or
Have a job that requires "swapping" of circuits from one panel to another. Past experience tells me that one must remove said circuits entirely from panel enclosure as it is not permissible to use a panel or disconnect enclosure as a raceway for other systems. I got to looking at 300.3 4C and 312.8 and it would seem to cover panel board enclosures so long as sufficient space exists for wire fill. Thoughts?

2017 / 2014 NEC & Related Books and Study Guides
Re: Panel enclosure as raceway [Re: bman] #170371
11/01/07 08:05 PM
11/01/07 08:05 PM
B
bman  Offline OP
Member
Joined: Jul 2006
Posts: 20
or
Guess its a good thing this didn’t come up on anyone’s Journeyman’s test.

Re: Panel enclosure as raceway [Re: bman] #170427
11/02/07 08:12 PM
11/02/07 08:12 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 845
Michigan
408.2 says 312 applys so I;d say yer right . Long as space is there.

Re: Panel enclosure as raceway [Re: Yoopersup] #170456
11/03/07 12:26 PM
11/03/07 12:26 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".


Greg Fretwell
Re: Panel enclosure as raceway [Re: gfretwell] #170546
11/05/07 05:11 PM
11/05/07 05:11 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Originally Posted by gfretwell
Just be aware a lot of AHJs take the first part of that sentence seriously "Enclosures for switches or overcurrent devices shall not be used as junction boxes" and they may want you to show that the listing for that enclosure and panelboard did provide "adequate space for this purpose".


You can't just take the first part of a sentence and ignore the rest.

You are allowed to use a panel as a jbox provided you meet the rest of 312.8 and unless you are really loading up the panel with splices or it is an older smaller panel there should be plenty of room.

Re: Panel enclosure as raceway [Re: Electricmanscott] #170561
11/05/07 09:50 PM
11/05/07 09:50 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,254
Estero,Fl,usa
Scott, If I was looking at this and it was done in such a way that did not clutter up the panel too bad I wouldn't have a problem with it but I know some guys who dissagree and have a very limited interpretation of what 312.8 allows.
I have even heard more restrictive spins on this in IAEI seminars from respected road warriors.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,684 Are you busy
186,422 Re: Forum
175,905 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.003s) Memory: 0.9770 MB (Peak: 1.1263 MB) Zlib enabled. Server Time: 2018-08-21 22:16:28 UTC