Smurf #169962 10/21/07 08:36 PM
Joined: Mar 2004
Posts: 777
B
BigB Offline OP
Member
I have rarely used Smurf, or ENT. I have a job coming up where it would really come in handy to get a couple of dozen circuits thru a very low attic crawlspace. Looks like I can fit up to 13 #12 AWG THHN's in a 3/4". This would mean 3 runs, 8 circuits apiece (using shared neutrals & 1 grounding conductor). After de rating I would still be good for 21 amps. Question is, anyone here ever put 13 (stranded)
12's in a 3/4" Smurf? The runs will be straight and about 75 feet.

Thanks.........B

Work Gear for Electricians and the Trades
Re: Smurf [Re: BigB] #169967 10/21/07 11:56 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
I don't think I have ever tried that many but I have done quite a few. Here in the land of 3:12 attics with a foot of "blow in", smurf is pretty handy stuff. The Carlon guy gave us a pitch on Smurf a while ago and he says you have your best luck if you strap it down straight and tight and strap all curves to hold the shape (not "belly"). Then you tape a "bullet" on the end and push the wires through.


Greg Fretwell
Re: Smurf [Re: gfretwell] #169968 10/22/07 07:50 AM
Joined: Oct 2005
Posts: 40
G
gibbonsseabee80 Offline
Member
BigB,
To be honest, I do not like smurf tubing. We had around 200 feet of 1/2" laying around in the shop. It was never outside, just old from sitting in the shop. It would crack and was very brittle. When you would swing it lightly, it would crack in half. Otherwise, I think you are fine as long as you apply the derating factor in there.


Brian Gibbons
Re: Smurf [Re: gibbonsseabee80] #169977 10/22/07 11:57 AM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
I am surprised at that. Maybe it is a "cold" thing. I have a piece of 3/4" sleeving the steering cable on my boat and it has been in the sun and salt water for 10 years. I have it on the trailer now and it still seems to be doing OK


Greg Fretwell
Re: Smurf [Re: gfretwell] #169979 10/22/07 03:25 PM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
BigB - You may want to double checck you wire fill calcs. Your neutrals wires count too.


"Live Awesome!" - Kevin Carosa
Re: Smurf [Re: sparkyinak] #169983 10/22/07 07:35 PM
Joined: Oct 2007
Posts: 56
S
SP4RX Offline
Member
He calculated fine, assuming that this is a three-phase installation. That would allow one neutral for up to three circuits. Thus for 8 ccts. : 3 ungrounded conductors
1 neutral
3 more ungrounded conductors
1 more neutral
2 final ungrounded conductors
1 final neutral
1 bonding conductor
---------------------
12 total conductors in conduit

The math seems good to me.

Shawn.

Re: Smurf [Re: SP4RX] #169985 10/22/07 07:58 PM
Joined: Jul 2004
Posts: 9,569
G
gfretwell Offline
Member
Even single phase comes up with 13 (2 hots and a neutral times 4 plus EGC) and that is the max in table 9 for #12 THHN in 3/4 ENT.
If this is really a straight shot and the ENT is pulled tight enough not to belly it should go in OK.


Greg Fretwell
Re: Smurf [Re: gfretwell] #169988 10/22/07 08:36 PM
Joined: Aug 2007
Posts: 853
L
leland Offline
Member
How much lube you got? and how many guys to pull?

Wink,Wink, smile

I actualy got that answer once as a helper.
I didn't like the thought, so I bought a code book.

And I have never cheated !! (Wink,Wink :))

Re: Smurf [Re: BigB] #169992 10/22/07 09:31 PM
Joined: May 2005
Posts: 10
P
plcnewbie Offline
Junior Member
Why not use MC home run cable
Stocking Sizes Color Codes:
Conductors 120 Volt Colors
6c black, black/silver, red, red/silver, white, white/silver
8c black, black/silver, red, red/silver, blue, blue/silver, white, white/silver
12c 3 black, 3 red, 3 blue, 3 white; each color numbered 1-3
16c 4 black, 4 red, 4 blue, 4 white; each color numbered 1-4

www.alliedtube.com/electrical-raceways/cable-systems/home-run-cable.asp

Re: Smurf [Re: leland] #169993 10/22/07 09:43 PM
Joined: Mar 2004
Posts: 777
B
BigB Offline OP
Member
Yes it is single phase, 2 hots to a neutral, one grounding conductor, comes to 13 conductors, 8 of them counted as current carrying.

Ran 4 runs today by myself, took me 6 hours (told you it was tight up there). Got them nice and straight, no "bellys". came out to 60 feet each.

My helper and I will pull in the conductors tomorrow then I'll report back.

Brian Gibbons, thst stuff must have been REALLY old or defective. The stuff I got is tough as can be. I have a roll of 1/2 inch thats 5 years old, still tough. I wouldn't be afraid to use it for a tow rope!

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,453 Are you busy
209,361 Re: Forum
196,636 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3