aldav53 Offline OP
Member
I had to rerun a pool pump and pool light circuit for a pool at a home. It also has a gas heater which needs 120v to it. Can I tie that into the line side if the GFI (light) circuit. I don't think its code to use half the 240v pool pump ckt, 120 v side, with the GFI line in for neutral. Is it? So I would be sharing the 120v side of the pool pump circuit for the control panel on the gas pool heater, doesn't draw much, but couldn't find it in the code book. Line side of the pool light circuit would probably be ok.

Last edited by aldav53; 10/17/07 12:21 AM.

The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
If you had a neutral it could be on that circuit (pump),(210.4(C) ex2) in fact I think the gas heater instructions do say you should be on the pump circuit. The problem is you should also be sure the pump runs several minutes after the heat turns off so if you have a timer you will need a way to keep the pump going.


Greg Fretwell
Joined: Mar 2003
Posts: 48
G
GTE Offline
Member
Most pool heaters are 120/240 volts. The pool heater can be connected to the load side of the pump time clock.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
The only problem with using the pool time clock is the heater instructions say you need to run the pump for up to 15 minutes after the heat goes off. Whenever the heater is on in my pool there is a parallel circuit that holds the pump on and maintains that for 10-15 extra minutes (a fairly simple circuit discharging a big capacitor across a darlington, picking a relay)


Greg Fretwell
Joined: Mar 2003
Posts: 48
G
GTE Offline
Member
Greg,
That's why there is a fireman's switch in the time clock to shut the heater off 20 minutes before the pump.

Joined: Aug 2007
Posts: 853
L
Member
So, the "fire mans switch is auto?
I've done pool heat pumps but not boilers.
On the heat pumps there is an option for a relay/contactor that goes in paralel with the load (pump), to maintain temp.
Side note: They don't need GFCI,just the bond(in MA.) I thought that strange.

I would think that with the boiler the override and timeing relay would be standard if this crucial.

However I've done some looking at diagrams and I don't see that. Strange.

Joined: Mar 2003
Posts: 48
G
GTE Offline
Member
It is not a relay, it's a micro switch that is connected to the clock mechanism that shuts the lovo side of the heater off 20 minutes before the pump.

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
Yup The "fireman switch" just opens on the 24v to the whole unit. Since I wasn't sure what my timer was going to end up being I built the delay off on the pump separately, about as fail proof as I could make it. The 15 minutes is really overkill. After the gas goes off the water temp drops pretty fast. In a minute it is close to pool temp.


Greg Fretwell
Joined: Mar 2003
Posts: 48
G
GTE Offline
Member
"The 15 minutes is really overkill. After the gas goes off the water temp drops pretty fast. In a minute it is close to pool temp."

I agree.