IAEI magazine article about the 2008 #168446 09/05/07 01:03 AM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline OP
Member
This month's IAEI mag has a short article about some of the changes in 2008. It hasn't hit the web yet but I have my hard copy.


Greg Fretwell
2017 / 2014 NEC & Related Books and Study Guides
Re: IAEI magazine article about the 2008 [Re: gfretwell] #168465 09/05/07 12:12 PM
Joined: Mar 2005
Posts: 399
A
Alan Nadon Offline
Member
Greg,
Some praise what others condemn.

Not having a pen name to shield myself that is all I'm willing to say, although my views on 406.11 are well known.


Alan--
If it was easy, anyone could do it.
Re: IAEI magazine article about the 2008 [Re: Alan Nadon] #168472 09/05/07 07:57 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Well, if nothing else, let this new code be a reminder.

Opinions are like fingers ... most everyone has a handful or two. The 2008 Code has been published. It's done. Now the ball is back in OUR court.

First of all, there is no reason that your locality must adopt it, either in whole or in part.

Secondly, NOW is the time to get involved in the next cycle. Get those proposals in. Get the comments rolling. Drown committee members in your submittals.

Personally, I suspect we're not far from the NFPA getting a major wake-up call. That call will come in the form of their losing credibility, due to an overly ambitious code writing program. But that's just one of my 'fingers' laugh

Re: IAEI magazine article about the 2008 [Re: renosteinke] #168475 09/05/07 10:54 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline OP
Member
One of the things we will get bit with is the requirement of load management hardware if you have a generator and a transfer switch. It sure doesn't read like the user will be able to do his own load management.


Greg Fretwell
Re: IAEI magazine article about the 2008 [Re: gfretwell] #168476 09/05/07 10:56 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
hmm... didn't know about that one!

Re: IAEI magazine article about the 2008 [Re: gfretwell] #168501 09/06/07 05:43 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Greg, actually the only change will affect those using ATS's for Optional systems, if a MTS or load management is used it will be the same as it is now.

Here is the ROP

Quote
Report on Proposals A2007

— Copyright, NFPA NFPA 70

(B) System Capacity. The calculations of load on the standby source shall be made in accordance with Article 220 of by another method that is acceptable to the authority having jurisdiction.

(1) Manual Transfer Equipment. Where manual transfer equipment is
used an optional standby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time. The user of the optional standby system shall be permitted to select the load connected to the system.

(2) Automatic Transfer Equipment. Where automatic transfer equipment is used, an optional standby system comply with a or b.

(a) Full Load. The standby source shall be capable of supplying the full load that is transferred by the automatic transfer equipment.

(b) Load Management. Where a system is employed that will automatically
manage the connected load, the standby source shall have a capacity sufficient to supply the maximum load that will be connected by the load management system.



Roger

Re: IAEI magazine article about the 2008 [Re: Roger] #168511 09/06/07 09:41 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline OP
Member
Thanks, I didn't get that from the article. That is more reasonable than some of the discussions I have heard about this.


Greg Fretwell
Re: IAEI magazine article about the 2008 [Re: gfretwell] #168529 09/07/07 06:31 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Quote
Personally, I suspect we're not far from the NFPA getting a major wake-up call.

I think that the only thing that would get their attention is for a number of states to refuse to adopt the 2008 NEC.
Don


Don(resqcapt19)
Re: IAEI magazine article about the 2008 [Re: resqcapt19] #168542 09/07/07 11:09 PM
Joined: Jul 2004
Posts: 9,568
G
gfretwell Offline OP
Member
Florida says they are going to pass. The FBC did cherry pick a few things out and put it in the Florida code. One thing is they are going with the relaxed 680.26(C) rules (single #8 ring)


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,348 Are you busy
209,214 Re: Forum
196,517 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3