FEMA Grant Proposal #168408
09/03/07 06:10 PM
09/03/07 06:10 PM
Grover  Offline OP
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
I've been tapped to assist in writing a grant proposal to establish a Shelter / Operations system in rural Maine.

I have not surveyed the site yet, but it involves 3 buildings - Fire Station, Town Office, Gymnasium with space for cots and a full kitchen. I'm guessing 200A panels in each - all within 2-300' of each other.

I've done several large, portable gensets, but am looking for the company that sells a "universal" lockout - mechanical in nature - tailored to different panels (had a link in the old pc that got bit by lightning!).

My concept at this point is to built up a surplus trailerable genset, 100-200A/240V surplus genset - located central to the 3 buildings, install the lockouts, connect to external, building mounted connectors via TC cable and go from there.

Operation would need to be ready for summer (thunderstorm/lightning/hurricane damage) or winter (snow/ice storm damage). Local staff could perform regular startup to assure readiness.

Comments or suggestions?

Thanks!

Grov

Work Gear for Electricians and the Trades
Re: FEMA Grant Proposal [Re: Grover] #168415
09/03/07 10:01 PM
09/03/07 10:01 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I really doubt your idea will be acceptable to the engineer.

I am doing a similar job right now, and the genset, along with the transfer switch, were specified, and purchased direct. I just get to install them. The spec on the genset was extremely detailed; one detail specified the noise levels.

In this case, the generator will be 'exercised' as part of a maintenance schedule, by the firemen. Loads will be automatically transferred; other installs will have you use a 'load bank.'

Re: FEMA Grant Proposal [Re: renosteinke] #168420
09/03/07 11:28 PM
09/03/07 11:28 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
You may want to see the loads in the fire station before you do too much engineering for this. A 200 amp service does not sound big enough.

Also sounds like you would be trying to split the output of the generator and use it to power all 3 buildings. UIf you were to truly have a diasaster in the area you may need full power to all three buildings at the same time.

Re: FEMA Grant Proposal [Re: Jim M] #168422
09/04/07 12:56 AM
09/04/07 12:56 AM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
I think it will be wise to get the load demand figured out first before you slecting the generator size and also you have to becarefull with 3Ø system they can get very tricky here if the building system is on 208/120 Y system and you get the trailerable generator if that generator is wired for delta system verised to the building system.

the other thing that you say trailerable genny it will be wise have either ATS or MTS with interlock so you cant disconnected under the load unless you have very rugged pin and sleeve connector [ those are not cheap btw ]

and also you have to find out the load for crictal circuirt and normal load and with 3 breaker box that really can get tricky there unless you put 3 ats for each loactaion and have one master ats where you will plug in the generator is

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,899 Are you busy
184,236 Re: Forum
173,469 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9608 MB (Peak: 1.0934 MB) Zlib enabled. Server Time: 2018-05-24 23:24:34 UTC