Is there any code that states you can't run the fire alarm
speakers and pulls in the same conduit?

GETELECTRIC #167846 08/21/07 01:52 PM
Joined: Jan 2006
Posts: 60
R
Member
Not that I am aware of. CAN/ULC-S524 makes a reference to section 32 of the CEC which allows what you want to do.