Industrial 56" ceiling fan troubleshoot #167562 08/15/07 12:42 PM
Joined: Nov 2001
Posts: 45
B
bill woods Offline OP
Member
I am stumped! Here's the scenario. Two 56" 120V industrial ceilng fans in parallel. One speed control. These two fans are on phase one of a three phase system. Phase two and three are lighting circuits. All small loads. The fan closest to the rheostat drops out of service. Technician checks and the motor has been fried. Checks voltage while second fan is still running. Line to neutral reads 140V on load side of rheostat. Why? When the switch is in the "high" setting or the "low" setting voltage is 120V. When the switch is adjusted between these settings voltage reads 140V. Again why? I can't explain it to my staff cuz I am at a loss.

Work Gear for Electricians and the Trades
Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods] #167563 08/15/07 12:47 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
The speed control works by chopping up the AC waveform, such that it is no longer a nice clean sine wave. Unless you use a "True RMS" multimeter, non-sinusoidal waveforms cause very screwy AC voltage readings in most cases.

Recheck the reading using a good quality TRMS meter, such as a Fluke 87.

Re: Industrial 56" ceiling fan troubleshoot [Re: NJwirenut] #167564 08/15/07 12:55 PM
Joined: Nov 2001
Posts: 45
B
bill woods Offline OP
Member
The meter used was a Fluke 337. Brand new.

Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods] #167567 08/15/07 01:51 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
I'll join you in stumpedness, then....:)

Does the working fan change speed properly between the high and low settings?

When you say the motor was "fried", do you mean actual burnt windings/smell, etc., or just an open connection with no visible damage?

Re: Industrial 56" ceiling fan troubleshoot [Re: NJwirenut] #167569 08/15/07 03:31 PM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
Could this be an issue of an open neutral, causing the other loads on phases B and C to affect the voltage on phase A?


---Ed---

"But the guy at Home Depot said it would work."
Re: Industrial 56" ceiling fan troubleshoot [Re: EV607797] #167615 08/16/07 01:21 PM
Joined: Nov 2001
Posts: 45
B
bill woods Offline OP
Member
Tech's troubleshooting reports no open neutral, and the fan has an open connection with no visible damage. He also reports that the fan housings seem a little on the warm side.

Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods] #167616 08/16/07 02:02 PM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
I just wondering is that ceiling fan is shared with common netrual with other lines if that so i will suggest that the fan run it own netural and Ø line as well because the fan speed control have it own ' modifed sine wave ' reduced voltage connection

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Industrial 56" ceiling fan troubleshoot [Re: bill woods] #167620 08/16/07 03:22 PM
Joined: Oct 2004
Posts: 803
mxslick Offline
Member
Originally Posted by bill woods
Tech's troubleshooting reports no open neutral, and the fan has an open connection with no visible damage. He also reports that the fan housings seem a little on the warm side.


Sounds like just a defective fan motor from here. A shifting neutral would probably have fried the motor violently and also killed the speed control.

As for your voltage readings, take them with a huge grain of salt, so to speak. If the control is electronic, in addition to chopping the wavewform, it would possibly increase the voltage to compensate for lost motor torque.

OTOH, you could have also been reading "inductive kickback" from the other fan's motor. smile

And as for the housings seeming "a little on the warm side" remember a normally operating modern motor can safely run up to 40 deg. C above ambient, more than hot enough to burn your hands!! smile

Replace the bad fan and move one..... smile


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,758 Are you busy
209,667 Re: Forum
197,016 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3