ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
GFCI's pops in large numbers
by dsk - 10/21/21 02:03 AM
Need some info on Japanese outlets, 200V 15A
by andey - 10/20/21 08:05 AM
Wire sizing
by watersparkfalls - 10/19/21 07:27 AM
nec 110.3 (B)
by watersparkfalls - 10/19/21 07:09 AM
A 5-20(20a) receptacle is legal on a 15a circuit?
by libellis - 10/10/21 12:46 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 8 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#166265 07/16/07 11:23 PM
Joined: Dec 2006
Posts: 33
W
wacked Offline OP
Member
I have a question concerning motors and voltage drop. It is said that a motor will draw more as the voltage is decreased ( say from 120V to 115 volts and less to a point) The motor will try to maintain the design HP output. What happens when you have a very significant resistance such as a smaller and longer extension cord, How does this all come into play with total impedance of the motor with the addition of another significant resistance. I was told that the ampacity would increase so much that a breaker would flip, due to the fact the motor will draw more. On the other hand I am looking at the line loss on the way to the motor that would limit current as a whole. Other than physically trying this (which I may do)This all stems from a friend of mine telling me too small of a conductor will cause excess current in a line with a motor. Does anybody have any comments on this?

Joined: May 2005
Posts: 984
G
Member
The voltage available at the motor will be less, so the current will be higher. That can be enough to trip the breaker.

Now onward to the confusion...
When STARTING, the current draw at a lower voltage will be less (that's why we have reduced voltage starters).
When the motor is RUNNING, the current will be more.
At some point in that whole process; you'll likely exceed the rating of the breaker and whammo.


Ghost307
Joined: Sep 2003
Posts: 650
W
Member
I made a comment on this topic a couple of days ago:
http://forums.mikeholt.com/showpost.php?p=701799&postcount=33

Start with a hypothetical 100% efficient motor. The electrical power input exactly equals the mechanical power output. Now reduce the input voltage. If the mechanical output were to remain constant, and the efficiency were to remain constant, the current drawn would need to increase.

_Real_ motors are not 100% efficient. Change the voltage and you change the efficiency.
Real motors draw reactive power; change the voltage and you change the reactive current flow.
Real motors will change speed when the supply voltage changes, possibly reducing the mechanical load.
Real motors can _stall_, ending up right at that starting current situation described above.

Depending upon the specifics of the situation, a reduction in supply voltage can do anything from slightly reduce the current drawn by the motor, all the way up to causing the motor to stall and draw many times more current.

-Jon

Joined: Apr 2004
Posts: 349
Member
Wacked,

Think of a simple series circuit containing 3 resistances: R1 can represent the resistance of one lead wire (L1), R3 can represent the resistance of the other lead wire (L2 or Neutral), and R2 can represent the impedance of the motor. As you know, the total voltage drop accross the entire curcuit (equal to the source voltage) will be split proportionally accross the 3 resistances.

So if the resistance values of R1 and R3 are increased, say by providing smaller wire, then the voltage drop accross R1 and R3 will increase proportionally, and the voltage drop accross R2 (the motor) will decrease proportionally.

The result is the motor will see less voltage, and will draw more current to maintain the connected power requirement.

Hope that helps some.
Radar


There are 10 types of people. Those who know binary, and those who don't.
Joined: Dec 2006
Posts: 33
W
wacked Offline OP
Member
Yes I can see where you all are coming from. I just was thinking that with a significant voltage drop along the lines to the load that there would not be a large draw as a whole due to the resistance of the entire circuit. I guess if the voltage drop is large enough, and if it was not for the oc device we would have major heating of the winding... and this is a motor and not a baseboard heater...........

Joined: Jul 2004
Posts: 101
J
Member
Yes, motor loads react differently.
The issue is, motor torque is reduced by the square of the voltage reduction. So if you end up with just a 20% voltage drop for whatever reason, you have 80% voltage and your motor output torque just dropped to .80 x .80 = 64% of rated torque! Since it isn't likely that the load changed, the lower torque allows the motor to slow down more, meaning increased slip. More slip means more current draw to try to regain speed. In the worst case, more current draw means more voltage drop, means more torque loss, means more slip, means more current, more voltage drop etc. etc. until the breaker or overload relay trips.

Last edited by jraef; 07/19/07 03:08 AM.

JRaef

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 6
Popular Topics(Views)
284,715 Are you busy
217,341 Re: Forum
203,693 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5