#166245 - 07/16/07 04:23 PM Divisions / Zones  
okfixer  Offline
Junior Member
Joined: Jun 2005
Posts: 6
Sidney,Ne, USA
What are the benefits of using zone locations over the division method? In looking over what OSHA is about to implement in August, it seems you have more liabilty using zone locations. Just curious.

Thanks


Arc Flash PPE Clothing, LOTO & Insulated Tools

#166246 - 07/16/07 04:48 PM Re: Divisions / Zones [Re: okfixer]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
They are simply two slightly different approaches. The biggest difference is that the 'zone' system has a category for stuff that is ALWAYS in a hazardous exposure ... such as inside a gas tank. Many things rated "Class 1 Division 1" are not intended to ALWAYS be in such an atmosphere.

The other aspect relates to enclosure ratings. Many items - controls in particular - are of European make, and are specified in terms of "zone," rather than area. As with other enclosure ratings, the European classifications are not quite exactly comparable to NEMA designations.

Hazardous location practices are something that you really have to evaluate for each job, considering the specifics of each situation, and keep in mind the 'big picture.' There are several approaches that can be taken ... not all of them electrical ... and it's not always smart to mix approaches.

I suppose it's not so much a matter of using either the 'zone' or 'area' method. I think you pretty much have to use both.



Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 242
Joined: February 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.002s) Memory: 0.7454 MB (Peak: 0.8640 MB) Zlib enabled. Server Time: 2017-10-17 13:25:34 UTC